Motor is 600kW/3.3kV rated (Full Load-121Amp).
Motor start was given and it was observed that, after 10 sec motor found tripped on Instantaneous over current (IOC) and during this time current was recorded as 350 amps on soft starter and no voltage variation observed on Turbine Gen. control panel. Direction of rotation of motor was found reversed.
Instantaneous over current (IOC) is set as 700% and instantaneous over current start delay is set as 1 cycle.
The cables of two phases were interchanged on the soft starter to reverse the direction of rotation as required.
In the next attempt to start, the motor tripped within 10 secs of starting on Instantaneous Over-current. The current on the soft starter was observed to be 320 Amps. The direction of rotation was found to be correct.
In the second attempt, the motor tripped this time on Locked Rotor Current I2T after running for almost approximately 30 secs. The current on the soft starter was observed to be 190 amps at the time of tripping.
The rotor continued to rotate for more than 5 minutes after the tripping of the motor.
All current observations were made on the analog ammeter on the Soft Starter.
Q. What could be possible reason for motor tripping. Should LRC be increased from existing setting of 300% to 500%? Existing step timer is set to 7sec - should this be modified?
Good Answers: