Sitrans CU02 Alarm Unit with AS 100 Sensor

01/10/2011 6:29 PM

We have installed a Sitrans CU02 alarm control unit with Sitran AS100 acoustic sensor. The Sensor has been mounted on the Raw Coal Shute on the outlet of a Mill Coal Feeder. The Relay on the alarm control unit gives an alarm of Coal Flow Failure

Under alarm condition, the 'alarm' flag starts flashing immediately, indicating that the relay delay set to 5 seconds has started counting. If the alarm condition ceases before the relay delay expires, the flashing 'alarm' flag is aborted.

My problem is that the alarm/relay seems to follow the raw sensor signal which due to our process is moving about. When the majority of the signal is below the alarm setting a spike in the coal flow will rest the alarm/relay. In effect I want the spike not to reset the alarm and bring up the Coal Flow Failure Alarm until the majority of the signal is above the alarm setting.

Has anyone had any experience with this alarm system and how to get round a spike?

Register to Reply
Pathfinder Tags: AS 100 Sensor CU02 Alarm Unit
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#1

Re: Sitrans CU02 Alarm Unit with AS 100 Sensor

01/10/2011 8:05 PM

Damping is provided to slow the response of the display when rapid or minor fluctuations in the process or machinery operation are encountered. The greater the damping value (P86), the slower the response. (page 11 CU02 manual)

P-86 damping, display (1ƒ to 999), where ƒ = factory setting (page 18)

Register to Reply
Member

Join Date: Jan 2011
Posts: 6
#2
In reply to #1

Re: Sitrans CU02 Alarm Unit with AS 100 Sensor

01/11/2011 2:26 AM

Thanks for the reply.

I will try today adjusting P-86 but from what I can remember this only seems to adjusts the display and not the relay/alarm. Do you know if adjusting P-86 will give damping to the relay/alarm?

Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#3

Re: Sitrans CU02 Alarm Unit with AS 100 Sensor

01/11/2011 11:11 AM

I don't know and the manual doesn't say, like most manuals no longer provide a theory of operation.

So I strongly suspect, that like most instrumentation, the value in the display is the same value that is used for the decision for relay operation.

There are two independent damping factors, one for the display, the other for the retransmitting analog output. I would assume that the damping factor for the display affects the local relay operation.

Register to Reply
Member

Join Date: Jan 2011
Posts: 6
#4
In reply to #3

Re: Sitrans CU02 Alarm Unit with AS 100 Sensor

01/11/2011 3:59 PM

Thanks for reply

Had ago today at adjusting P-86 from 2 to 15 this had the effect of damping the display and giving a more stable reading. It seems that the 'alarm' flag is still going as fast as it was. From my tests adjusting P-86 is only damping the display

Take a look at this graph

Feeder Speed at 5 RPM the majority of the readings are at 50% with the odd spike going below the alarm setting of 40%.

Feeder now set at 3 RPM the majority of readings are at 25% with the spikes going above the 40% thus resetting the 'alarm' flag. These spikes are the ones that are causing us problems and not bring up the Coal Flow Failure Alarm.

Now looking at the 4 to 20 mA's output and have adjusted P-85 to 25. At this value the output looks stable, but still moving 0.1 to 0.2 mA's.

I am thinking of connecting a PR Electronics Trip Amp to this output and using that to bring the Coal Flow Failure Alarm. Seem a waste not to use the CU02 relay

Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#5

Re: Sitrans CU02 Alarm Unit with AS 100 Sensor

01/12/2011 10:56 AM

Is the graph a recording of the 4-20mA output? If so, what damping factor was applied during the recording?

Register to Reply
Member

Join Date: Jan 2011
Posts: 6
#6
In reply to #5

Re: Sitrans CU02 Alarm Unit with AS 100 Sensor

01/12/2011 4:30 PM

Thanks for reply

Quote "Is the graph a recording of the 4-20mA output?" =

The graph is the display reading in % values with P-86 (Display Damping) set at 2. At this setting the readings are bouncing about from 15% to 45%.

I have then adjusted P-86 to 15 and P-13 (Relay 1 delay) to 3 this then brings the display reading between 25 to 30 and a more stable readable value. The 'alarm' flag still comes up so resetting the alarm but the majority of the readings are below the 40% alarm setting. This should be bring up the Coal Flow Failure Alarm but with the spikes the 'alarm' is reset.

The Damping factor for 4 to 20 mA's on P-85 (mA's Damping) set to 25. At this value the output looks stable, but still moving 0.1 to 0.2 mA's

I now have the Trip Amp will install on the current output ... hopefully tomorrow

Register to Reply
Member

Join Date: Jan 2011
Posts: 6
#7
In reply to #6

Re: Sitrans CU02 Alarm Unit with AS 100 Sensor

01/14/2011 1:03 PM

I have today connected a Trip Amp to the CU02 output and using that to bring the Coal Flow Failure Alarm.

Its early days but so far looks promising

It just seems a waste not to use the CU02 relay

Thanks for your help