Transformer Question - Take Power in Any Direction

01/11/2011 4:26 AM

Is it possible to take power from a power transformer in any direction. For example normally a T/F primary will be connected in 132kV bus and its secondary feeds into 33kV Bus. Is it possible we can supply 33kV in same secondary side and take load in 132kV primary side. I heard that only auto transformer can do this kind of power reversal as it is having only one primary winding and secondary is taken as a tappings from the same winding.

Suggestion please

-Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Transformer question

01/11/2011 5:16 AM

Yes It is feasible

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#2
In reply to #1

Re: Transformer question

01/11/2011 5:20 AM

thanks for your reply.

Is there any extra changes to be done while it is being constructed or any transformer can be used immediately when required.

-Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #2

Re: Transformer question

01/11/2011 9:42 AM

How about OLTC to get fixed secondary voltage?.

__________________
pnaban
Register to Reply
Anonymous Poster
#3

Re: Transformer Question - Take Power in Any Direction

01/11/2011 8:51 AM

Power =voltage x current you are wrong with your question its not power you mentioned.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Transformer Question - Take Power in Any Direction

01/11/2011 1:25 PM

Transformers do not "know" the direction of transformation, it's strictly a matter of winding ratios for inductive coupling. It makes no difference if it's an autotransformer or an isolation transformer. But there are plenty of issues to consider when back feeding a transformer, including the configuration of the windings, i.e. Delta or Wye (Star) and the appropriateness of switchgear, protective devices etc. etc.. Some of those issues don't exist for autotransformers, some do. it requires a thorough understanding of the application, the equipment and the people who will service it to make a decision.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#6
In reply to #5

Re: Transformer Question - Take Power in Any Direction

01/11/2011 10:28 PM

ok but what abt the OLTC. How we will vary the voltage to get the constant output in primary side if we are back feeding it. If all the switchgears , equipment is made ready for the backfeeding, how about the voltage regulation. I seen in some of the OLTC stated that " This tapchanger is only to be used where power flow is from HV to LV"..

-Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #6

Re: Transformer Question - Take Power in Any Direction

01/12/2011 10:45 AM

Current limiter...voltage in, voltage out...up to down, down to up...doesn't matter. Must limit current through the transformer to prevent runaway. If you don't the breaker, a.k.a. current limiter (on/off discriminator) will.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8
In reply to #6

Re: Transformer Question - Take Power in Any Direction

01/12/2011 12:58 PM

In normal operation HV to LV, the tap-changer will keep LV voltage at its rated value , say +/-1%. But if input is from LV winding, this voltage varies +/-5% or more - values above normal could overflux LV winding (regardless of tap-changer posn on HV winding - hence "caution" in specification).

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#9
In reply to #6

Re: Transformer Question - Take Power in Any Direction

01/12/2011 1:51 PM

You must specify to the transformer manufacturer what the use of the transformer will be, so that the OLTC is set up to regulate the output of the "load" side appropriately. Usually OLTCs are used with transformation from higher to lower voltage, to feed distribution or plant loads.

If transformation is from lower to higher voltage, OLTC is seldom (I can't say never, but I haven't seen it) used. Such transformation is usually found in generating plants to step up to transmission voltages, and the voltage from the generator is usually adjusted via the generator controls.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#10

Re: Transformer Question - Take Power in Any Direction

01/12/2011 2:54 PM

I do this regularly. Some of my generation is directly connected to a distribution bus. When the generator is not running, the transformer supplies the distribution load from the transmission line on the high side. When the generator is running, it supplies the load on the distribution bus. Any additional generated power is stepped up through the transformer and sent through the transmission system to other substations.

Why do you feel you need a constant voltage on the 132kV side? I would be very surprised if its constant right now. I suspect it varies throughout the day due to changes in loading and voltage drop on the 132kV source. If the 132kV side is connected to a multi-generator grid you will need some way to control VAR flow, but an OLTC would be a complicated and unreliable way to do so. The OLTC controls are not designed to operate in that direction. You should already have voltage controls on whatever generator or transformer would provide the 33kV power to the transformer. Use those controls to manage your voltage and VAR flow.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard