3 Generator in Parallel

01/14/2011 4:01 AM

if the existing two generator are already synchronized by the use use of auto synchronizing panel and it need 1 more generator with the same rating.. how i can connect the new generator to the 2 generators?? is there a sync panel that can use for 3 generators??

any diagram, material or websites?? thx.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: 3 gennerator in parallel

01/14/2011 4:24 AM

This question was asked and answered recently. A paralleling panel can accommodate any number of generators. Whatever set of generators is already on line is taken as the reference voltage/ phase sequence/ frequency. The incoming generator is compared to the existing bus either by synchroscope or synchronizing lights (in various possible configurations, which need to be understood ahead of time); when the incoming generator matches the bus, its connecting switch or breaker is closed.

I apologize that this explanation is incomplete; more detail could be described.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: 3 Generator in Parallel

01/14/2011 6:00 PM

The function of the synchronizer is to verify the synchronizing conditions and connect the generator to the system bus if the conditions are full filled. Once the generator is connected to the bus, the synchronizer remains idle.

Generally synchronizer is used in two fashioned:

(1) A single common synchronizing panel is used and it is wired to the system so that you can select it for synchronizing any of the generators to the system. In this case, selector switches are used to select the synchronizer for each of the generators.

(2) Individual synchronizing panel is used for each of the generators.

You first check how the synchronizer system is configured and then find how to synchronize the 3rd generator to the system.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)