Max. Motor starting capability of DG set

01/14/2011 5:44 PM

What are factor to be considered for sizing DG set for industrial application regarding max rating of Sq. cage induction motor which can be started DOL.

Is there exist some standard which can be followed.

For example a DG set of 1000KVA operating and delivering load of 300 KVA, what can be biggest size motor be started on it.

Some suggest half capacity available of DG set. For given example (1000KVA - 300KVA)/2 = 350 KVA or 297 KW at 0.85 pf.

Pl share experience and suggestion

__________________
When was last time you did something for first time.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Max. Motor starting capability of DG set

01/14/2011 6:10 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2
In reply to #1

Re: Max. Motor starting capability of DG set

01/15/2011 1:49 AM

Thanks MS for your reply

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7
In reply to #2

Re: Max. Motor starting capability of DG set

01/16/2011 4:47 PM

You had several responses that are correct.

Simply: The remaining available power divided by 6 will be adequate most of the time.

Don't forget that a DG rating should include a surge capacity for several seconds and an overload capacity for an hour. these will help take care for the very short time demand of more than 6 times the normal nominal current of the motor (~ 10 times for DOL).

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #7

Re: Max. Motor starting capability of DG set

01/17/2011 6:24 AM

Thanks.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#3

Re: Max. Motor starting capability of DG set

01/16/2011 6:10 AM

It depends upon the amount of energy held in the weight of all the rotating mass (Flywheel etc) as to how big an overload can be supplied for a second or two.....

But I used to work with 6:1 as a rule of thumb. This would allow a motor to start without stalling or noticeably slowing the prime mover.....

That is I needed the motor not to exceed about 1/6 of the generator max load.....

Motor and starter design play a significant role and should not be forgotten, as the right combination will/may allow a slightly larger motor to be safely started.

It is as good as impossible to use the fully Alternator output with motors, the generator will always be "lightly" loaded, except at big motor start time.....that you have to accept.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#4

Re: Max. Motor starting capability of DG set

01/16/2011 11:32 AM

A 1000 KVA DGset is already supplying a load of 300 KVA. It means the genset capacity available for motor startup is 700 KVA. A squirrel cage motor draws about 6to 8 times of its rated current at start up depending upon the starting load conditions. Hence, approx 1/8th of the balance capacity i.e. approx 90KVA OR 90 HP motor can be DOL started. But again the number of starts you can have in a given time will also be limited and the genset supplier is the best advisor. The max capacity of the DOL started motor will also depend upon the engine and the governor characteristics and here again the engine manufacturer needs to be consulted. The inertia of the load coupled to the motor will also play an important role in making this decision.

PRIYADARSHAN

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5
In reply to #4

Re: Max. Motor starting capability of DG set

01/16/2011 12:10 PM

Isn't that what I said in my post? Mine is simply written and uses less words.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#6
In reply to #4

Re: Max. Motor starting capability of DG set

01/16/2011 3:42 PM

Dear P,

I disagree with your explaination to question. Pl refer more appropriate reply of msamad.

__________________
When was last time you did something for first time.
Register to Reply
Commentator

Join Date: Feb 2006
Posts: 55
#8

Re: Max. Motor starting capability of DG set

01/16/2011 9:59 PM

check your mail box and revert back i can send you the application and installation of DG sets

murali

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#10

Re: Max. Motor starting capability of DG set

01/17/2011 8:37 AM

One thing is the ability of the generator to recover during motor starting.This depends upon the AVR.Most motors in India are designed to accelerate at 80% Voltage.So a drop below this can stall the motor.You can calculate the voltage and a rule of thumb is tolimitit to 20%.So sizing has to be done accordingly.This holds good for low inertia applications like pumps etc.But if a high inertia is involved then one has to do detailed calculations including the acceleartion time, The drop , recovery time of AVR all have to be seen.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (3); Happy singh (2); LAA_Lucke (1); msamad (1); murali (1); nesubra (1); Priyadarshan (1)

Previous in Forum: Defy 620 Cooker   Next in Forum: For Turbo Generator Protection
You might be interested in: KVA Meters, Motor Test Equipment, Motor Repair Services

Advertisement