What to Do With Opened Out Put of Live CTs?

01/15/2011 6:28 AM

I have an Energy Meter at main DB and 3 CTs 400/5A are connected with it. I want to remove the Meter for repairing but what to do with CTs, should I short their points or leave them open after disconnecting the Energy meter?

What possible happen if i leave their out put points open?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: What to do with opened out put of live CTs?

01/15/2011 6:40 AM

Smells that you want to test our knowledge, about which you know something already.

Reply
5
Active Contributor

Join Date: Dec 2010
Location: visakhapatnam, India
Posts: 11
Good Answers: 2
#2

Re: What to do with opened out put of live CTs?

01/15/2011 6:44 AM

Before you remove the energy meter, you must short the CT secondary terminals in the Terminal block. CT shorting link arrangements must be available in the terminal block. Never open CT secondary when the CT primary is carrying current. If it occurs, the voltage across the secondary rises to a huge value. Due to the absence of back emf the working flux increases and the core gets saturated. This leads to overheating and the CT finally will fail or a flash-over can occur.

Reply Good Answer (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: What to do with opened out put of live CTs?

01/15/2011 7:01 AM

What total stinking idiot voted this as off-topic? It is exactly and importantly correct.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: What to do with opened out put of live CTs?

01/15/2011 7:35 AM

i agree, so my GA to take it further after you have negated that OT vote.

Maybe the first button being OT and the second one being GA, people inadvertently vote wrong ? i think Admin should make the GA button more prominent than the OT button.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: What to do with opened out put of live CTs?

01/15/2011 8:00 AM

Excellent. Pravinba is now honored. It is probably too much to hope that his/her critic will acknowledge this.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7
In reply to #2

Re: What to do with opened out put of live CTs?

01/15/2011 9:32 AM

I also agree this is exactly the right answer (one more GA). But there is the possibility of some non-standard wiring without the shorting link terminal available. In this case, either (1) short it from CT secondary terminal or (2) do the replacement work at de-energized condition. But option 2 is preferred for safety consideration.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: What to do with opened out put of live CTs?

01/15/2011 8:26 AM

I'll add to the score.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#8

Re: What to do with opened out put of live CTs?

01/15/2011 10:19 AM

Pravinba is the real OP.

Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#9

Re: What to Do With Opened Out Put of Live CTs?

01/16/2011 2:12 AM

simple... you short them out

Next question please!!

Reply
Anonymous Poster
#10
In reply to #9

Re: What to Do With Opened Out Put of Live CTs?

01/16/2011 5:49 AM

Is italian prime minister silvio berlusconi guilty??

Reply Score 2 for Off Topic
Anonymous Poster
#13
In reply to #10

Re: What to Do With Opened Out Put of Live CTs?

01/18/2011 12:43 AM

This made me laugh...

Yes, he is.... mostly of being Italian and breathing!!

NEXT!!

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#11
In reply to #9

Re: What to Do With Opened Out Put of Live CTs?

01/17/2011 9:04 AM

Yes, but you short them out before disconnecting the load (the meter or whatever).

Reply
Anonymous Poster
#12
In reply to #11

Re: What to Do With Opened Out Put of Live CTs?

01/18/2011 12:41 AM

I personally would have the supply/power/load isolated, disconnect the DEAD CT's, short them out and THEN continue. Nearly 40 years in the electrical game and I AVOID working in live panels as MUCH as possilble.

Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#14
In reply to #12

Re: What to Do With Opened Out Put of Live CTs?

01/18/2011 1:03 AM

Sensible i know. But rather disappointing for a design engineer. i spent considerable time perfecting the shorting-link system for many withdrawable equipment - MCCBs, ACBs, Relays ... believe me, some of them were tested to ridiculous levels for establishing reliability.

Still, your advise is very much valid. Unless there is extreme difficulty in interrupting main power.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#15
In reply to #14

Re: What to Do With Opened Out Put of Live CTs?

01/18/2011 7:49 AM

I agree with you (GA from me)since,it is not desirable to switch off the feeder just for replacing a defective meter ,particularly in production shops/industries.Further,special terminal blocks with sliding type shorting links for CT wring are available in the market which are easy & safe to use.

__________________
Learning is a never-ending process.
Reply
Reply to Forum Thread 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); kvsridhar (2); msamad (1); pravinba@yahoo.com (1); rhkramer (1); spradhan (1); thccontrols (1); TonyS (1); Tornado (2)

Previous in Forum: Anyone Knows About DSC & TGA   Next in Forum: HVAC Mimic