rated surge voltage for testing power cables (LV,MV)

01/15/2011 4:34 PM

I want to know the rated surge voltage for testing the low and medium voltage faulty cables.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: rated surge voltage for testing power cables (LV,MV)

01/15/2011 5:55 PM

What are the actual voltages these cables are due to carry?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jul 2009
Posts: 26
#3
In reply to #1

Re: rated surge voltage for testing power cables (LV,MV)

01/16/2011 10:23 AM

Rated voltages for low voltage = 1000/600 v and the medium voltage cables are 6.6 and 11 KV rated.

You know that the surge energy proportional to the test voltage and to get high acoustic effect I have to raise the test voltage to the cable limit (in case of high noise)

Thanks for replaying me

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4
In reply to #3

Re: rated surge voltage for testing power cables (LV,MV)

01/16/2011 4:29 PM

As said before, you need to check the standard specifications relevant to your country.

The test voltage depends on several things like the insulation thickness...

I found the following link to a pdf file with British standard specifications, (go to page 6 for a quick view if relevant to your request).

http://gjbz.ugcn.cn/%E5%9B%BD%E5%A4%96%E6%A0%87%E5%87%86/%E6%AC%A7%E6%B4%B2%E6%A0%87%E5%87%86/20100225/2/bs%205099-2004.pdf

Register to Reply
Associate

Join Date: Jul 2009
Posts: 26
#5
In reply to #1

Re: rated surge voltage for testing power cables (LV,MV)

01/17/2011 1:51 PM

for low voltage 400 volt phase to phase and for M.V 6.6 and 11KV phase to phase

Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#2

Re: rated surge voltage for testing power cables (LV,MV)

01/15/2011 10:44 PM

If you are a manufacturer the minimum requirements will be defined in national power cable standards that are applicable to your location. If you are a user, refer to the same standards and the manufacturer's literature and specifications.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#6

Re: rated surge voltage for testing power cables (LV,MV)

01/18/2011 3:54 AM

Dear Sir,

Surge voltage( THUMPING ) is injected in faulty cables to PIN POINT cable fault in underground cables. Generally maximum surge voltage injected from a SURGE GENERATOR is five times of the rated voltage of the cables. However, this voltage is depending on various factors like age of the cable, condition of earthing of armours, no. of joints, age of the joints, condition of end terminations,depth of laying,etc.

__________________
Manindra