I want to know the rated surge voltage for testing the low and medium voltage faulty cables.
Re: rated surge voltage for testing power cables (LV,MV)
01/15/2011 5:55 PM
What are the actual voltages these cables are due to carry?
01/16/2011 10:23 AM
Rated voltages for low voltage = 1000/600 v and the medium voltage cables are 6.6 and 11 KV rated.
You know that the surge energy proportional to the test voltage and to get high acoustic effect I have to raise the test voltage to the cable limit (in case of high noise)
Thanks for replaying me
01/16/2011 4:29 PM
As said before, you need to check the standard specifications relevant to your country.
The test voltage depends on several things like the insulation thickness...
I found the following link to a pdf file with British standard specifications, (go to page 6 for a quick view if relevant to your request).
http://gjbz.ugcn.cn/%E5%9B%BD%E5%A4%96%E6%A0%87%E5%87%86/%E6%AC%A7%E6%B4%B2%E6%A0%87%E5%87%86/20100225/2/bs%205099-2004.pdf
01/17/2011 1:51 PM
for low voltage 400 volt phase to phase and for M.V 6.6 and 11KV phase to phase
Good Answers: 27
01/15/2011 10:44 PM
If you are a manufacturer the minimum requirements will be defined in national power cable standards that are applicable to your location. If you are a user, refer to the same standards and the manufacturer's literature and specifications.
01/18/2011 3:54 AM
Dear Sir,
Surge voltage( THUMPING ) is injected in faulty cables to PIN POINT cable fault in underground cables. Generally maximum surge voltage injected from a SURGE GENERATOR is five times of the rated voltage of the cables. However, this voltage is depending on various factors like age of the cable, condition of earthing of armours, no. of joints, age of the joints, condition of end terminations,depth of laying,etc.
Manindra