like OCR in Air Circuit breaker and different individula type relay in electrical protection system
Good Answers: 804
Re: Difference Between Relay and Release
01/16/2011 1:06 PM
I'm not completely sure of your question, but I think you are asking what is the difference between a "relay" and a "release" when describing a protective function in a piece of distribution equipment?
If so, a relay would be a stand alone device that monitors for the condition and sends a signal to be acted upon by another device, such as a contactor or circuit breaker. A "release" of the same name is usually referring to the fact that the circuit breaker has the protective function built-in to it.
So for example, a circuit breaker may have an "Under Voltage Release" (UVR) built into it. That means if the voltage to the coil of that UVR is eve below the hold-in threshold, it lets go and activates the trip mechanism of the breaker. But an Under Voltage Relay (which may also be abbreviated UVR) would be a separate relay monitoring for a specific threshold of line voltage and taking action based on programmed parameters. Those actions however may not necessarily involve tripping the breaker, it may just send an alarm to a SCADA system.
The same could be said for an Over Current Relay, although the concept of an Over Current Release would be inherent in any circuit breaker, so I have never actually seen that listed separately.
India - Member - New Member
Good Answers: 164
01/16/2011 9:04 PM
JRaef is quite right. Here is the definition from IEC 60947-1:
01/17/2011 12:42 AM
Release is something which release your CB to operate or like a mechanical interlock.
Relay is a protective device and it comes into the picture only after the CB closed.
You don't understand anything until you learn it more than one way.
Good Answers: 170
01/18/2011 11:59 AM
Relay:
Mounted external to the breaker
Needs shunt trip coil on the breaker
Needs trip supply
Needs interconnecting wiring
Relay operationg time is more tahn a release
Release:
Integral part of the breaker
Direct acting (does not need a shunt trip coil on the breaker)
No need of trip supply
No need of inter connecting wiring
Operating time less than that of relay
03/19/2018 12:44 AM
For UV does UV release auto close upon resumption of voltage?