like OCR in Air Circuit breaker and different individula type relay in electrical protection system

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Difference Between Relay and Release

01/16/2011 1:06 PM

I'm not completely sure of your question, but I think you are asking what is the difference between a "relay" and a "release" when describing a protective function in a piece of distribution equipment?

If so, a relay would be a stand alone device that monitors for the condition and sends a signal to be acted upon by another device, such as a contactor or circuit breaker. A "release" of the same name is usually referring to the fact that the circuit breaker has the protective function built-in to it.

So for example, a circuit breaker may have an "Under Voltage Release" (UVR) built into it. That means if the voltage to the coil of that UVR is eve below the hold-in threshold, it lets go and activates the trip mechanism of the breaker. But an Under Voltage Relay (which may also be abbreviated UVR) would be a separate relay monitoring for a specific threshold of line voltage and taking action based on programmed parameters. Those actions however may not necessarily involve tripping the breaker, it may just send an alarm to a SCADA system.

The same could be said for an Over Current Relay, although the concept of an Over Current Release would be inherent in any circuit breaker, so I have never actually seen that listed separately.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Difference Between Relay and Release

01/16/2011 9:04 PM

JRaef is quite right. Here is the definition from IEC 60947-1:

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#3

Re: Difference Between Relay and Release

01/17/2011 12:42 AM

Release is something which release your CB to operate or like a mechanical interlock.

Relay is a protective device and it comes into the picture only after the CB closed.

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Difference Between Relay and Release

01/18/2011 11:59 AM

Relay:

Mounted external to the breaker

Needs shunt trip coil on the breaker

Needs trip supply

Needs interconnecting wiring

Relay operationg time is more tahn a release

Release:

Integral part of the breaker

Direct acting (does not need a shunt trip coil on the breaker)

No need of trip supply

No need of inter connecting wiring

Operating time less than that of relay

Register to Reply
Member

Join Date: Jan 2012
Posts: 9
#5

Re: Difference Between Relay and Release

03/19/2018 12:44 AM

For UV does UV release auto close upon resumption of voltage?

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); JRaef (1); kvsridhar (1); spikenet (1); vijaymail_electrical (1)

Previous in Forum: Electrical Engineering   Next in Forum: Generator Parameters

Advertisement