Hi all, im trying to spec this generator, looking at the datasheet for it, Xd (synchronous unsaturated reactance) is missing. I'm modelling the generator on SKM, and it has Xd as a per unit input which it links with the base kVA and voltage of the generator. Shouldn't Xd=1 pu? Since Xd is the steady state unsatured reactance which is computed from the base kVA, base voltage and hence base current?
Electrical Engineer
Re: Generator Parameters
01/17/2011 10:51 PM
I have the same problem
01/18/2011 5:21 AM
My assumption was wrong, S=V^2/Z, where S=rated kVA, V=rated voltage, Z=Load+Xd (load = load placed on generator terminals to draw S(rated))
Electrical Engineer
02/11/2012 7:38 PM
Here's what I've found with LV generators. Using the default values makes almost no difference in using manufacturer's s.c. data. I deal alot with regulatory bodies such as ABS, USCG, DNV, BV, and on & on where most use 10 time the aggregate generators connected and 3-4 times the total motor loads. I wouldn't lose any sleep over it.