Generator Breaker

01/17/2011 1:50 AM

Please kindly advise the reason why not install the generator breaker for steam turbine Generator in CCPP power plant while Gas turbine generator has his own breaker(52G).

Station power is supplied from Aux. transformer which locates between Gas turbine generator and it's step-up transfomer.

Thanks,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#1

Re: Generator Breaker

01/17/2011 1:57 AM

you mean there is no CB available for steam gen. is it? then how will they protect the gen if there is no CB in its outgoing... could you please be more specific...

__________________
You don't understand anything until you learn it more than one way.
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Generator Breaker

01/17/2011 2:25 AM

Common Generator + Transformer overall differential protection (87GT) is economical and is very commonly applied thereby a generator CB is purposeless.

Generator CB is manufactured by a few manufacturers and is very expensive.

Since the Aux Transformer is there with the Gas Turbine the designer had no choice but to provide individual differential protections for the generator as well as main transformer, while the generator CB has been installed to cover for short circuit faults in station power supplies link.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Generator Breaker

01/17/2011 3:01 AM

I once worked in a remote fish plant with a 5-genset powerhouse. The gensets were connected to the bus via CBs in the switchboard. There was a short circuit in the wiring between one genset and its CB. There was lots of "magic smoke" as the engine bogged down trying to feed this fault, which also smoked one vertical section of the switchboard and browned out my refrigeration system. Within a day, our electrician cleaned out all the residues with Boraxo, and wired in a spare genset we had.

One might think that mounting the CB on the genset itself would have prevented that, but then the fault would have been fed from the bus side, which could have been worse. Vibration might also be an issue for genset-mounted CBs, which may be a reason for not having CBs on both ends.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#4
In reply to #3

Re: Generator Breaker

01/17/2011 6:42 AM

Well said. ( Give me GA next time)

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Generator Breaker

01/18/2011 12:29 PM

What are the capacities & voltages of the Steam Turbine Generator and Gas Turbine Generator?