Use of NGR

01/18/2011 12:08 AM

Hi all,

I have a query regarding use of NGR. As per my knowlegde, NGR is used to prevent the fault current entering into the equipment in case of Line to Ground fault in the outgoing of the equipment such as gen, Trafo, motor etc. Also, it also used to limit the fault current flowing into the ground. But this works only in case of trafo. What abt in case of generator, bcoz the fault is occuring next to the source and the generator will start feeding the fault and in this case how the NGR limits the fault current.

Please correct me if i am wrong.

-Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Use of NGR

01/18/2011 12:36 AM

Search Neutral Grounding resistor or NGR in this forum, there are lots of threads on the subject.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#2

Re: Use of NGR

01/18/2011 12:45 AM

NGR is the sound I make when I am really frustrated about something (but with a few more Rs, like NGRRRRRRR!)

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Use of NGR

01/18/2011 1:05 AM

It is language dependent....we Bangaloreans go AYYYAYYYYOOOOO !

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#4
In reply to #3

Re: Use of NGR

01/18/2011 1:42 AM

Ha! Thanks for the good laugh!

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply Off Topic (Score 5)
Anonymous Poster
#5
In reply to #3

Re: Use of NGR

01/18/2011 3:51 AM

Pick the balls others dropped!!!!........

Register to Reply Score 2 for Off Topic
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Use of NGR

01/18/2011 4:40 AM
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#7

Re: Use of NGR

01/18/2011 9:21 AM

Draw out a 3-phase elementary drawing of the system. If there is a NGR in the generator neutral, any fault to ground that is fed by the generator would have to flow back through the resistor. The value and thermal capacity of the resistor are sized to handle the limited current (for example, 400 amps for 10 seconds, plenty of time for protective relays to operate).

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Use of NGR

01/18/2011 12:16 PM

I fear your understanding is a weebit incorrect. The purpose of NGR is to reduce the fault current during an earth fault (it could be an L-G fault or an L-L-G fault too). It will work well both in case of transformers as well as in the case of generators. More so in generators, as the single line to earth fault current in generators can be more than the three phase fault current and thus, it obviates the need for an NGR to limit the single line to ground fault current fed by a generator. More concerns would also be towards core damages in rotating electrical machines like generators during an internal line to ground fault.

Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#9
In reply to #8

Re: Use of NGR

01/18/2011 10:52 PM

What u told is correct. But how it will limit the fault current. Bcoz resistor is placed in the neutral and current flows from the generator. You mean since the neutral is the nearest free path for current flow, it will try to flow thro that path. So if we place the resistor in the shortest path, the fault current will find difficult to flow.

Am i right?

-Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply