Damper Pot

01/19/2011 6:51 AM

There is pressure transmitter for measuring "P" in reformer fire box in my application.

Range is min -50mmWC to +5mmWC.

One leg og PT is connected to PROCESS whereas one leg of it is connected to damper pot containing air with ambient conditions.

I am not clear abt the concept behind using damper pot in this case..

Could anyone explain plz.

__________________
Be happy :)
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Damper Pot

01/19/2011 10:48 AM

It's probably to slow down the response of the transmitter to process conditions, though what does the site Instrumentation Maintenance Supervisor have to say about it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#2

Re: Damper Pot

01/19/2011 3:50 PM

A little more information on the instrument itself might be helpful.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
5
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#3

Re: Damper Pot

01/19/2011 8:24 PM

For us non-metric guys, the cited range is approximately -2.0"w.c to 0.20" w.c.

Transmitters in this range are sometimes referred to as draft range transmitters.

The DP readings at this low range can be affected by moving air on the reference side, either as direct pressure on impulse tubing or as a venturi effect across the opening of a impulse tube.

I suspect that a damping pot is a chamber designed to damp air movement in the reference side impulse tubing that would otherwise be misinterpreted by the transmitter as pressure changes.

I've seen scintered filters on the end of impulse tubing or capillary tubing used for impulse tubing in order to damp reference side pressure fluctuations.

Register to Reply Good Answer (Score 5)
Commentator

Join Date: Oct 2009
Location: Michigan
Posts: 73
#4
In reply to #3

Re: Damper Pot

01/20/2011 9:27 AM

Thanks Carl...

__________________
Be happy :)
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Carl_E (1); msn (1); PWSlack (1); RDGRNR (1)

Previous in Forum: Displacer Level Transmitter   Next in Forum: Burnout Settings in a Transmitter
You might be interested in: Damper Actuators, Rotary Dampers, Industrial Magnets

Advertisement