Burnout Settings in a Transmitter

01/19/2011 12:22 PM

How to give burnout settings in a transmitter in the following cases:- a) when the transmitter is used for low low trip b) when it is used for high high trip Also please clarify in burnout settings what is fail safe or fail to trip in burnout settings

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Burnout Settings in a Transmitter

01/19/2011 1:23 PM

Can you please explain what you mean by 'burnout setting' as I have not come across this.

Do you perhaps mean transmitter failure mode?

__________________
jack of all trades
Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#2
In reply to #1

Re: Burnout Settings in a Transmitter

01/19/2011 8:11 PM

"Burn-out" is common terminology in thermal processing industries.

The term is used in the configuration of instruments or controllers to which thermocouples or RTD's connect, like field transmitters or analog inputs on PLC's, DCS's, single loop controllers, Process Automation Controllers (PAC's), indicators or recorders.

The term is used to define output action of the transmitter or the analog input function block in the event that the input loses its sensor signal, i.e. the sensor circuit goes to an open circuit condition. An open circuit infers that the input sensor, thermocouple or RTD, has "burned out", been disconnected or has had a signal wire cut. The loss of a valid sensor signal is indicated by driving the indicated input signal either full down scale or full up scale.

In heating applications, the loss of a sensor input is generally (not always) upscale burnout, which drives a controller's PID or ON/OFF output to zero because the PV (temperature) is too hot, hence the control output is reduced, presumably to safe levels.

Some digital indicators will 'flash' digits to indicate a fault. The signal disappears upscale or downscale on a recorder. Low or high alarms are tripped, depending on burn-out direction.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Burnout Settings in a Transmitter

01/20/2011 4:36 PM

Ah! A sensor fault (i.e. <4mA or >20mA).

Well, most programmable electronic systems have a facility with which to raise an alarm should something like this happen.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#4

Re: Burnout Settings in a Transmitter

01/26/2011 4:30 AM

for low trip - Burnout feature shall be upscale i.e., 20 mA

for high trip - Burnout feature shall be downscale i.e., 4 mA

this is because to ensure fail safe condition burnout feature shall be opposite of trip condition.

Reply
Power-User

Join Date: Jun 2008
Location: beverly hills
Posts: 116
#5
In reply to #4

Re: Burnout Settings in a Transmitter

02/04/2011 4:57 AM

Hi, Guest

Basically this burn-out configuration it is depend on the process requirement?

Regards