Genset to Power Grid

01/21/2011 5:47 AM

We produce 20L of waste fry oil from our business each week. Would like to use waste oil as biodiesel through my small (8kva) genset and provide energy to the power grid reducing our power bill. I have no electronical monitoring equiptment. (portable genset only)

Q..... Would this be a finanially viable setup with the equipment I need, and if so, what equiptment is it that would have me up and running.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: genset to power grid

01/21/2011 5:59 AM

If you wish to synchronize with the grid, this will involve some fairly expensive equipment (and probably some negotiation with your electrical utility). If you can find some loads that match your biofuel generation capacity, and remain stand-alone with those loads, it will probably be simpler. No one solution fits all cases, but it will be good to research this as well as you can.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#2
In reply to #1

Re: genset to power grid

01/21/2011 7:50 AM

Tornado, what would be the downside of generating a DC voltage to feed a grid-tie inverter? I know it's converting twice, doubling the inefficiency, but at least he's getting something out of the waste oil and it's easier than trying to synchronize a genset.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#3

Re: Genset to Power Grid

01/21/2011 10:15 AM

Maybe you could rethink your savings scheme in terms of removing equipment from the grid and using the genset for power in a standalone fashion.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: Genset to Power Grid

01/21/2011 1:07 PM

The simplest grid tie route is to use your engine to spin a standard AC induction motor faster than it normal runs when connected to your AC lines. It then becomes a self synchronizing grid tied generator system.

Start your engine and bring it up to speed and then connect to the lines, thats it.

I will let the legality and safety Nazi's/worrywarts take it from here.

Register to Reply
Anonymous Poster
#5

Re: Genset to Power Grid

01/21/2011 2:16 PM

I had an 8000 watt pull recoil start genny. It had one 120 volt duplex receptacle and one 240 volt receptacle on it. On occasion I would back feed my home breaker panel, 240 volt genny to 240 volt service via a 30A, 2P circuit breaker. With no load I would watch the utility meter run backwards. When I would initially bring it on-line, the generator RPM would rapidly fluctuate up/down 50 - 100 RPMs. After about 30 – 40 seconds, the rapid RPM fluctuation would begin to smooth out and within 60 seconds, the generator would be running perfectly smooth. Never popped a circuit breaker nor the on board push button reset. Was this luck or was the genny able to sync up because it was producing such a small output? Obviously, connecting to the grid without the proper equipment is dangerous but theoretically, couldn't shanewaldoc connect directly to the grid as I did?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #5

Re: Genset to Power Grid

01/21/2011 4:37 PM

For your information :-

  1. Connecting a generator 180 degrees out of phase to a big-rating supply takes twice as much current as short-circuiting it. This causes four times the bursting force in the windings compared to a short circuit. Big generators are only designed to survive short circuit.
  2. Small generators are less efficient than big ones - they have relatively more resistance to limit the current. There is also more weight of copper (better able to absorb the excess heat) in a small machine relative to rating.
  3. You were obviously running at the right speed, else this would have been worse (a generator is a very bad motor for self-starting - without special provision like an auxiliary induction motor winding, although once synchronized they make good motors).
  4. The rpm fluctuation was because the synchronizing forces on the rotor cause an angular oscillation of the rotor about the final speed which takes a long time to damp down.
  5. You are probably at the end of a long local line which means you get voltage dips if you apply exceptional loads - this limits the current.
  6. Depending on the class, a 30A breaker can take 100s of amps to trip it off instantly. Below this, in its thermal overload mode, the breaker is designed to trip for over what the feeder cables can take.
  7. Small things are stronger - if an aeroplane flies into a building, both are wrecked. If a wasp flies into a window, it bounces off and tries again!
  8. Theoretically, couldn't shanewaldoc connect...... If his supply is much stiffer it could be wrecked generator and breaker.
  9. If I had to do it, I would put electric fire bars in the feed to the generator, rated for full voltage (Short-out with switch once it all stabilizes) : equalize voltage, speed/phase, as close as possible using voltmeter and synchronizing lamps before closing breaker. The firebars are a precaution against gross error, it worked for Mr Westinghouse (without firebar) over a century ago!
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#7

Re: Genset to Power Grid

01/22/2011 1:30 AM

What is your business? Lighting loads should be fairly constant. Waste heat AND electricity could heat your water for dishwashing, clean-up, building heat. Twenty liters isn't much energy. What's the diesel consumption at 8kva? Work out the cost of converting the fry oil to biodiesel. It's complicated and messy. Better to sell the oil and pay your electric bill. And look into solar thermal water heating for restaurant business. It's the best payback time.

__________________
Align culture with nature...
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#8

Re: Gen-set to Power Grid

01/22/2011 3:32 AM

shanewalddock; Go for it. you could use light bulbs for synchronizing the gen set, one your locked in, speed up your engine till you see your output from the gen set, this should slow down your watt-hour meter. DOWN SIDE!! if your power company were to lose power to your building, you would be feeding power back into the power co. line & injure or kill a employee! MAYBE the circuit breaker on the gen set would trip with the increases load. perry

Register to Reply
Power-User

Join Date: Oct 2007
Posts: 102
Good Answers: 8
#9
In reply to #8

Re: Gen-set to Power Grid

01/22/2011 11:31 AM

The lamps for synchronising need to be twice the circuit voltage, (to take the mains plus alternator voltage at 1890 degrees). The supply co here would prosecute you if you were caught; seems a big risk.

Bigger downside; If your supply feeder breaks your alternator could feed wiring and shock or electrocute someone. Maybe manslaughter!

Better feed a diesel vehicle or isolated electrical load.

Register to Reply
Participant

Join Date: Jan 2011
Posts: 2
#10

Re: Genset to Power Grid

01/22/2011 10:53 PM

Thanks to all for your fantastic help and support. We're leaning towards using the genset as a pwr backup to the cold rooms.

What a great site and thanks again!

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11

Re: Genset to Power Grid

01/23/2011 1:43 PM

Would like to use waste oil as biodiesel through my small (8kva) genset and provide energy to the power grid reducing our power bill.

For the simplest and most financially viable alternative, convert the waste oil to biodiesel and use it in one of your diesel company vehicles!

Initial equipment costs are much, much lower (no expensive grid-tie inverter needed) and some double conversion inefficiencies are also removed. Additionally as it would be used for a company vehicle it can be classed as a business expense.

__________________
jack of all trades
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (1); jack of all trades (1); Lo_Volt (1); ormondotvos (1); perry (1); RDGRNR (1); shanewaldock (1); tcmtech (1); Tornado (1); Zaf (1)

Previous in Forum: DG Cable   Next in Forum: I Need 5Vac From Distribution Transformer Line.

Advertisement