01/21/2011 3:31 AM

what is the correct rating for 750 kva dg

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: dg cable

01/21/2011 3:40 AM

What voltage?
What ambient temperature?
What type of insulation on the cable?
3-core cable, separate cables, all cables in one conduit/raceway?
Any other conductors in the same conduit/raceway?
What code are you following?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: dg cable

01/21/2011 4:04 AM

Voltage-415, Delhi ambient tem-42degree C

insulation -XLPE

If 3 or 3.5 core--

If single core---

In trench

No conductor cable except control cables,

Indian standard

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: dg cable

01/21/2011 4:43 AM

Excellent; that is the information needed to proceed further.

750,000 VA/(415√3) ≈ 1043 A; this is the most critical number. For continuous duty, you may need to multiply by 1.25, giving 1304 A. If you use cable, I think you will need to parallel at least 3 or 4 cables (unless you do this with bus bars).

I am not familiar with IS (India Standard), but in the U.S. NEC (National Electrical Code) there are several tables giving the allowable current for various conductor sizes and types and insulation temperature ratings. You must take care in consulting the correct table for the conditions. If you use multi-core cable, each cable should contain all 3 phases.

I have only hit a few high spots here, so please consider this as just a start. I don't have a code book in front of me, and thus can't go much further at the moment.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Member

Join Date: Dec 2010
Posts: 6
#4
In reply to #3

Re: dg cable

01/21/2011 6:28 AM

if i use as suggested by dg vendor 3.5C,300sqmm xlpe cu condutor with armoured as under:

R, Y , B & N Cores of Cable-1 will get terminated to Terminal "R" of the generator,

R, Y , B & N Cores of Cable-2 will get terminated to Terminal "Y" of the generator,

R, Y , B & N Cores of Cable-3 will get terminated to Terminal "B" of the generator,

R, Y , B & N Cores of Cable-4 will get terminated to Terminal "N" of the generator,

I may go for bus bar what the distance between DG and Panel is 100Mtr.Approx

Lets suggest

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: dg cable

01/21/2011 9:46 AM

Why not keep it simple:

  • All the reds to the R terminal
  • All the yelows to the terminal
  • All the blues to the terminal
  • All the Ns to the N terminal

?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #4

Re: dg cable

01/21/2011 10:50 AM

Please get a more knowledgeable vendor. PW Slack is correct; we have said the same basic thing in two ways.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7
In reply to #4

Re: dg cable

01/21/2011 3:27 PM

You already posted this under "Cable Sizing". In my opinion 4 cables of the size you give will be adequate if they are well spaced apart and on a perforated tray, in the open and protected from the sun. BUT using armoured cables with only one phase in them is BAD practice which will lead to overheating and failure. Use the "three core and neutral" cables with all 3 phases and a neutral in each cable as they are intended to be used - you will not be buying any more cables than proposed. Also, as one correspondent noted, extra copper is wasted on the neutral, that is why the neutral is half the section.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (1); GULSHAN KUMAR (1); PWSlack (1); Tornado (3)

Previous in Forum: Frequency   Next in Forum: Genset to Power Grid
You might be interested in: KVA Meters, Cable Laying Services, Cable Assemblies

Advertisement