Recomputing of Loads

01/21/2011 7:07 AM

What do you called the term where you count all the loads of all building, listing the rating of all loads like aircon, convinience, lights etc.. so you will know the actual apparent power.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Recomputing of Loads

01/21/2011 8:22 AM

Load schedule...

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Recomputing of Loads

01/21/2011 10:50 AM

Actual Power? Apparent Power? There is some confusion here, at least in my mind. Please clarify.

i believe you are looking for "DIVERSITY FACTOR". In India and IEC countries, this is <1, being the sum total of all loads which are likely to be ON at any one time.

There are many threads in CR4 on this, please search.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Recomputing of Loads

01/21/2011 2:28 PM

How about determining the "connected load".

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Recomputing of Loads

01/21/2011 10:12 PM

Here's an example: Suppose you have a main pump and a standby pump, but only one of them runs at a time. They both are connected loads, but they are not concurrent. You can size the total system on the basis of maximum concurrent (rather than connected) load.

Sometimes you don't know for sure what the total concurrent load would be. Say you have an apartment building all on one service. Not all of the washers, dryers, AC units, and stoves are likely to be running at once. But if your code allows it, you can apply a "diversity factor"; i.e., some percentage of the total connected load. In the U.S. the code specifies the diversity factors you can use for various numbers of apartment units. It might be like 80% or so.

(The terms "real power" and "apparent power" refer to something else; namely, "power factor," which has been discussed many times on CR4.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#5

Re: Recomputing of Loads

01/22/2011 2:56 AM

dhanking23; tornado was the closest to what you were asking. if you had a 40 unit apt building, you would not figure 40 times electric ranges @ 8000 watts each, or 40 electric dryers @ 5000 watts each! look in the 2011 national electrical code hand book for the de-rating figures that they list. perry

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); kvsridhar (1); perry (1); Tornado (1); wareagle (1)

Previous in Forum: I Need 5Vac From Distribution Transformer Line.   Next in Forum: Lux Lumen Calculation
You might be interested in: Electronic Loads and Load Banks

Advertisement