Anonymous Poster

Power Cable Selection

01/24/2011 5:38 AM

respected sir, Here i want to select a power cable for a mechinery 850kw,380volt,50hz.Is there any formula to select power cables, please help me as soon as possible.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#1

Re: power cable selection

01/24/2011 5:46 AM

There are multiple factors which must be taken into account during calculating the cable such as;

1) What is the length of cable (>100mtrs de-rates the cable)?

2) How to lay, direct in ground or in open air? (temperature factor)

3) Are there any more cables in the route of this cable (grouping factor)

4) What is the max temperature of the area where it would lay?

5) Would the cable be armored or simple?

__________________
Don't assume any thing, always check/ask and clear yourself
Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#2
In reply to #1

Re: power cable selection

01/24/2011 6:18 AM

Hello signode, Op asked for formulae and not for your advice.

Reply Off Topic (Score 3)
Participant

Join Date: Jan 2011
Posts: 1
#7
In reply to #1

Re: power cable selection

01/25/2011 5:48 AM

1) length of the cable is 25mtr 2) lay the cable in ground but through pvc pipe 3) yes,two cables 6mm & 5mm respectively 4) maximum temperature is 40c 5) i would like to lay armored cable

Reply Off Topic (Score 5)
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: power cable selection

01/24/2011 7:52 AM

Try looking in BS7671 and save us the trouble of helping you

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 2)
Active Contributor

Join Date: Jan 2011
Posts: 10
#4

Re: power cable selection

01/24/2011 7:58 AM

Hi,

If it's a motor use I=p/root 3*V*cosphi

Reply
Anonymous Poster
#5

Re: Power Cable Selection

01/24/2011 12:26 PM

I

the suitable cable depend on the distance between source and equipment so for power 850 kw 380 thecable

if distance not more than 150 feet is 185 mm,if distance not more 75 feet 95mm,if distance not

more 300 feet the cable is 400mm in metric system best regards

assuming tempreture 55 c

ENG salman

Reply Off Topic (Score 7)
Anonymous Poster
#6
In reply to #5

Re: Power Cable Selection

01/25/2011 4:09 AM

dear Engineer salman,,...what the XXXX?

Reply Off Topic (Score 5)
Participant

Join Date: Jan 2011
Location: mumbai
Posts: 3
#8

Re: Power Cable Selection

01/27/2011 7:03 AM

FOR 850KW THE CURRENT CARRYING CAPACITY WILL BE 1500AMPS.SO YOU CAN USE 300SQMM OF ALUMINUM OF EQUAL LENGTH

Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#9

Re: Power Cable Selection

02/17/2011 7:27 AM

What kind of machinery? Anyway, for normal load of 850KW, 415V, 50Hz, and PF = 0.8 :

I = 1480A

Icb(%age) = 1700A

The standard manufacturer size of CB = 2000A

And the cable size required would be:

11 X 1C X 630 mm^2 XLPE/SWA/PVC/CU + 2 X 1C X 300 mm^2 PVC/CU/ECC

:-)

__________________
--
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#10
In reply to #9

Re: Power Cable Selection

02/18/2011 2:19 AM

Now again, you may also use a CB size of 1600A and the cables,

8 X 1C X 630 mm^2 XLPE/SWA/PVC/CU + 2 X 1C X 300 mm^2 PVC/CU/ECC.

But for machinery high inrush current, selecting CB of 2000A would be a better choice. It seems a little oversizd, though?

__________________
--
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#11
In reply to #9

Re: Power Cable Selection

04/25/2011 5:21 AM

You have failed to mentioned the machinery type?

__________________
--
Reply
Reply to Forum Thread 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

abasins (3); Alanvaderi (1); Anonymous Poster (2); joanaphiri (1); kunhonm (1); SHABU (1); Signode (1); TonyS (1)

Previous in Forum: Capacitor Bank   Next in Forum: How to Calculate Steam Flow Rate for Following Condition

Advertisement