Capacitor Bank

01/23/2011 10:40 PM

what should be the location of Capacitor bank. Either It should be installed at HT side or LT side?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Capacitor Bank

01/23/2011 11:04 PM

LT.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2
In reply to #1

Re: Capacitor Bank

01/23/2011 11:27 PM

But my coin says HT side. What does LT mean to you?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Capacitor Bank

01/23/2011 11:54 PM

LT = 0-1000v; HT > 1000v (where they say "tension" rather than "voltage") [?]

I don't know what the KPU (Ketchikan Public Utilities) voltage into our transformers is; but our 80kvar PF capacitors are on the 480 low voltage side, paralleled to their respective 450-hp motors.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14
In reply to #3

Re: Capacitor Bank

01/25/2011 7:35 AM

GA

Adding: In theory, correcting the PF for the Power Utility benefit, it does not matter where you correct it as long as it reduces the losses on the distribution lines. BUT It is cheaper and easier to produce LT capacitors.

Also, usually, the LT is toward the consumer, and the PF correction must be nearest to the point where it is most consumed, otherwise, it is still feeding down the line and still produces losses upstream!

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#15
In reply to #14

Re: Capacitor Bank

01/25/2011 8:09 AM

Regards.

Your points are valid but I have been working on Users systems; not on Power Suppliers; in all cases the PF Correction on LT side is the responsibillity of consumers and Suppliers ensure it on their side on HV side [In my country it is 11KV].

About GenSets I have little info but on UPS Systems we have PF Correction Module on almost all systems greater than 110KVA systems.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#13
In reply to #2

Re: Capacitor Bank

01/25/2011 7:13 AM

I agree with you as in Pakistan we see on the 11KV Poles not on Street poles distributing to houses.

Register to Reply
Anonymous Poster
#4

Re: Capacitor Bank

01/23/2011 11:55 PM

Dear Sandeep, Did you calculated cable for lighting load?... Didi you have any design drawings for your project?...Are you the responsible person for designing?...

Register to Reply
Active Contributor

Join Date: Jan 2011
Location: Madhya Pradesh- India
Posts: 13
#5
In reply to #4

Re: Capacitor Bank

01/24/2011 12:30 AM

No, i have yet decided type of fixtures and lumainaires for the project

Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#6
In reply to #5

Re: Capacitor Bank

01/24/2011 5:38 AM

Normally consumer installs cap at LT side, they are not responsible for HT. The power supply company installs cap at HT side.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Active Contributor

Join Date: Jan 2011
Location: Madhya Pradesh- India
Posts: 13
#7
In reply to #6

Re: Capacitor Bank

01/24/2011 6:25 AM

But since we have to improve power factor on 11KV side as our major load is on 11kv side, so it has been considered to install capacitor at 11KV side instead of 415V side.

Register to Reply
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#8
In reply to #7

Re: Capacitor Bank

01/24/2011 9:34 AM

I'm sure someone more knowledgeable will reply, but I can make a few observations. First, to perform its power-factor-correction job, considering impedance-scaling through the transformer, in theory the physical bulk size of the required capacitor will be the same on either side, and hence the cost the same. This is because of the scaling of the capacitor-insulation thickness, etc., and the way capacitors of different voltages but with equal stored energy tend to have the same volume. All other things being equal.

But I speculate that two things argue in favor of the secondary side. First, caps on the HV side will probably need more insulation because they're closer to HV transients, whereas the leakage inductance of the transformer limits its high-frequency response, protecting the secondary capacitors. So primary-side caps will need higher safety margins and be more expensive. And second, the transformer will experience a better power factor if you apply the correction on the secondary side, so it can have lower peak-current ratings.

__________________
Thanks, Win
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #7

Re: Capacitor Bank

01/24/2011 10:46 AM

Maybe they do things differently in your location, but here the electrical meters are on the secondary side, as are the PF capacitors, if any.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#10

Re: Capacitor Bank

01/24/2011 11:11 AM

People here have forgotten one critical thing that I think tips the choice to putting the capacitor bank on either side of the transformer. The transformer core reluctance limits the amount of fault energy that can be transferred per cycle. So I believe the capacitors should reside on the load and not the power distribution side of the transformer. So if this transformer is stepping up the line voltage from the grid then the capacitors should be applied to the HT side.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Anonymous Poster
#11

Re: Capacitor Bank

01/24/2011 10:59 PM

THIS DEPENDS ON SYSTEM REQUIREMENT.

1.CAPACITOR BANKS ARE BASICALLY LOCATED NEAREST TO THE INDUCTIVE LOAD CENTRE AND IN THAT CASE IF THERE IS HT LARGE MOTORS THIS CAPACITOR BANK SHOULD BE LOCATED NEAR HT SWBD OR THERE SHOULD BE SVC UNITS.

2.FOR LT LARGE MOTORS THIS CAPACITOR BANKS SHOULD BE NEAREST TO THE MOTOR OR LT SWITCHBOARD.

3.FOR LARGE FURNACE TRANSFORMERS SAY 33KV/---V 150MVA RATINGS AND ABOVE CAPACITOR/SVC UNITS WITH PROPER HARMONIC SUPPRESSOR UNITS ARE LOCATED IN 33KV BUS ONLY.

IN A NUTSHELL CAPACITOR BANKS TO BE LOCATED NEAREST TO THE LOAD CENTRE .

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#12

Re: Capacitor Bank

01/24/2011 11:53 PM

Mr. Sandeep k.v,

Mr. Winfield Hill and Mr. redfred imparted their brilliant engineering knowlwdge, so you've got the perspective view to exactly where to install the capacitor/s and what capacitor bank meant to you in relevance to power factor correction. The transformers are getting its power source directly from power generating plants and need to step-up the line voltage/s into transmission lines over head system, first we installed reactor on HV 132kv side to maintain primary line currents. Again in our case here we have 5000MW power plant(PP9)(Saudi Electric-SCECO) that delivers 2.40kv and then step-up into 132kv, then steps down to sub-distribution voltage system at 13.80kv 3-phase in HV/MV substation/s. The capacitor bank are installed at 13.80kv load distribution side feed to another MV/LV substations at 13.80kv/380v-3-phase for consumers... reason why it need to install capacitor bank on load side is to maintain or correct the power factor of the line that feed to consumers/load.

__________________
If there is a will... there is a way... No pain / No gain.
Register to Reply Score 1 for Good Answer
Member

Join Date: Dec 2010
Location: India, Gujarat, India
Posts: 6
#16

Re: Capacitor Bank

01/25/2011 11:33 AM

Normally, the use of capacitor bank is for correction of power factor. The more closer to load , more is the effect of Capacitor bank. Now, irrespective of that, if we put capacitor bank to HT side for the same effect, voltage rating of Capacitor bank will increase, which will further increase the cost of capacitor bank,requiring greater insulation level, protection for capacitor bank, termination, cable for capacitor bank etc. Hence techno-economically, It is best to put Capacitor bank LT side.

Register to Reply
Participant

Join Date: Jan 2011
Posts: 4
#17

Re: Capacitor Bank

01/27/2011 11:50 AM

in the load side

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#18

Re: Capacitor Bank

04/16/2017 11:43 AM

Dear Mr. sandeepkv,

There are 2 isssues here.

1st issue is the LT supply consumer - responsibility lies with the consumer and hence the capacitor bank as for as possible should be closer to the motor and the KVAR required, as thumb rule, in general will be (0.4) x H.P. of Motor or (0.543) x KW - where the PF will be around 0.8

2nd Issue is in the limits of Power Supply Agency who maintains HT Transformers for Distribution and they have to install the Capacitor in their premises on HT input side.

Dhayanandhan.S

Register to Reply
Register to Reply 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!