How to Calculate Reinforce Concrete Foundation

01/25/2011 7:01 AM

hi, all

how to calculate reinforce concrete foundation?

please guide thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#1

Re: How to Calculate Reinforce Concrete Foundation

01/25/2011 3:36 PM

1. Calculate load on footing.

2. Get allowable bearing pressure from soil report.

3. Determine footing area required.

4. Decide on shape. Simplest is square but not always possible.

5. Calculate shear and bending moment.

6. Determine depth to satisfy shear.

7. Determine reinforcement to resist bending moment.

__________________
Bruce
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#2
In reply to #1

Re: How to Calculate Reinforce Concrete Foundation

01/25/2011 3:56 PM

And at number 8:

Send CR4 member ba/ael a cheque for engineer services!

__________________
Semper Ubi Sub Ubi
Reply
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#3
In reply to #2

Re: How to Calculate Reinforce Concrete Foundation

01/25/2011 4:47 PM

Thanks, Doorman.

__________________
Bruce
Reply
Anonymous Poster
#4
In reply to #3

Re: How to Calculate Reinforce Concrete Foundation

01/26/2011 8:09 AM

I was at a dinner party the other night at the yacht-club when a guy asked everyone at the table for structural engineering services to design or retrofit a column to support a beam where apparently a bearing wall had been or is scheduled to be removed.

As the only Registered PE (Civil) involved in the conversation, I quickly lost interest in bidding on these "services" as the client seemed to be more interested in a "quick and dirty solution" than a proper approach as you outline (to which I strongly endorse as necessary steps).

It seems other non-professionals were encouraging the prospective client to put the column on top of the existing slab (typically 4-inch non-reinforced concrete) rather than to remove a portion, excavate for, and place a proper footing.

When I tried to steer the conversation in that direction, the response seemed to be that such steps were not considered because they would require too much work (excavating a footing below an existing slab by hand, etc., would be troublesome).

Alternative plans to span the slab with plate steel to distribute the load (hoping not to punch through the slab) were then suggested by the arm-chair "Engineers".

After the Client (an unemployed airline pilot) received his "Broken Propeller Award" (this was an awards dinner) for the most spectacular grounding of the 2010 season, he again began discussing his problem of "where am I going to find a Registered Structural Engineer to stamp my drawings. But by this time, I had lost interest in the project and him as a prospective client.

Bruce, how do you deal with such issues?

The other question is whether in such cases, a Registered Civil Engineer could stamp the work involved here (or must he be Registered Structural Engineer). Had the client been willing to play by the rules (as you outlined), I might have considered the work.

Of course, I would want to get paid. No more free work for friends or acquaintances.

ps - I am not self-employed, but work for a large agency in the USA. I rarely stamp engineering drawings now in this position (although I maintain the licenses in several States).

Reply
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#5
In reply to #4

Re: How to Calculate Reinforce Concrete Foundation

01/26/2011 12:40 PM

"Bruce, how do you deal with such issues?"

I usually try to convince the arm-chair engineers of the proper way to deal with the situation. If that doesn't work, I try to change the subject. Sometimes you just can't win.

The question about who can stamp structural drawings varies from state to state. For an issue as simple as the one you describe, I would think that most states would permit a Civil Engineer to seal the documents, but I am no authority on engineering regulations in the USA.

In Alberta, Canada where I have practiced most of my life, any engineer can seal any drawing because our association (APEGGA) does not register by discipline. Needless to say, we are expected to perform only those services for which we are competent. Those who don't may find themselves facing a lawsuit, a disciplinary hearing or both.

Doing "freebies" for friends or relatives should be avoided unless you are prepared to accept full responsibility for the consequences. Even casual advice from you to the pilot over cocktails about the depth or size of his footing can get you in trouble if he acts on it without taking into account that the footing is sitting on five feet of uncompacted fill, a fact he omitted to mention to you.

By the same token, I avoid specific design requests on this or any other forum which ask for the required size of footings, columns, beams, joists or other members for a particular structure which the OP is building in an unknown location with unknown snow loads, wind loads and unknown seismic requirements. The OP is fishing for free engineering instead of retaining the professional help he needs.

__________________
Bruce
Reply
Anonymous Poster
#6
In reply to #5

Re: How to Calculate Reinforce Concrete Foundation

01/26/2011 1:43 PM

Thanks Bruce, great advice.

As a R.P.E. Civil, I would have been comfortable certifying a very simple footer design, but not for my wife's friends or folks I meet over drinks!

I would never get involved in more complicated structural steel building design under any conditions as that would be out of my area of expertise (as you point out).

I did successfully change the subject for an hour or so, but this guy left that evening still convinced that he would find someone willing to play his game (up until about 10 years ago my state (MA) was very lax in this regard, but they have cracked down quite a bit recently looking particularly at work done out of discipline and also stamped without fully supervising the work of others not certified.

This Captain/Commercial Pilot/Contractor spent a lot of time blaming his mate for running into the rock while he attended to matters down below (in this 26 foot Sail/auxiliary vessel).

In presenting the "Broken Prop Award", he was asked why he did not keep watch on his crew knowing that this was his responsibility and one to be deferred to others.

I can just see him throwing the Structural Engineer under the bus when this building collapses!

Another interesting aspect to the puzzle regards the Construction Supervision issue. Hypothetically, suppose a valid design is prepared, certified, and approved, but then substantial changes are made during construction which result in a system failure? The Contractor may try to point to you as negligent or in error while you may be forced to defend the design as an undocumented field change.

It would seem that in such a case, you would have to be present to witness the work prior to backfill or in the case of reinforced concrete construction prior to concrete placement.

May get to be a very slippery slope from a liability standpoint.

But I digress.

Very good comments. Hopefully others will take heed!

Reply
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#7
In reply to #6

Re: How to Calculate Reinforce Concrete Foundation

01/26/2011 3:22 PM

If a valid design is modified on site and the modification results in system failure, the Engineer must be able to defend his design. The Contractor cannot show him to be negligent or in error unless he is. This can be proven conclusively when the cause of the problem is discovered.

It is best that construction be inspected by the Engineer prior to covering it up. Soil should be examined prior to pouring footings. Reinforcement should be inspected before placing concrete. There are times when this is not done because of conflicting schedules, but in these cases, it is wise for the Engineer to protect himself by asking the Contractor to provide photos of the uninspected work. It may not be an ideal solution, but it is better than nothing.

In my experience, most contractors are prepared to co-operate with the Engineer of Record in attaining a good job which everyone can be proud of. Those who are not should be dismissed immediately (not always easy but necessary).

__________________
Bruce
Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#8

Re: How to Calculate Reinforce Concrete Foundation

01/27/2011 12:03 PM

I Second the Motion to cut a large retirement-sized CERTIFIED CHECK for him! hehehehe I'm terrible aren't I????? *GRINZ*

As always, a great answer. Damn it man, you must have lightning-fast typing fingers, as you are always beating me to the punch with your super quick postings! I don't stand a chance! LOL You and that great engineering Guru from Egypt!

GA from me on your 1st posting!

Keep up the great works (and answers)!!!!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#9
In reply to #8

Re: How to Calculate Reinforce Concrete Foundation

01/27/2011 12:11 PM

Thanks, CaptMoosie. Don't know about lightning-fast anything at my age, but I am really looking forward to that retirement-sized certified check. Beats a GA anyday.

Have you been keeping up with the snow shoveling in your area?

__________________
Bruce
Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#10
In reply to #9

Re: How to Calculate Reinforce Concrete Foundation

01/27/2011 12:43 PM

Thanks ba for asking. We got snow storm #7 last night, but it didn't amount to much of any consequence. About 3 inches. Now we have about 3 feet on the ground. I still have to remove the remainder of snow and ice off of the solar PV panels and roof yet....at least 4 inches of ice atop 4 or so inches of snow. On top of it all is 2 feet of fresh snow! Unfortunately my 21 foot long snow rake won't reach the upper portions of the panels and roof ridge! more ACCKKKK ACCKKK! We're praying for a very quick thaw here shorty.There's no sign of the thermometer rising over 32F within the next week. Damn!

I'm getting tired of digging out of this White Chit frankly...too damn cold and no room to put it all! hehehehe Thank goodness we have snow plow services to get rid of the stuff out of the long long driveway, otherwise they'd probably find me frozen the snowbank sometime during the Spring thaw, Moose hair withstanding!

How the weather up your way. I just imagine the Winter Wonderland you folks have to endure, eh?! Please keep warm my friend, keep VERY warm! Spring is just 2 months away, ohhhhh myyyyyy!

As they say, the check is in the mail....just don't hold your breath waiting for it okay? Yeah, I've been stiffed by clients, friends and family too! Deadbeats all!

Have a great day.....now off to the Dentist appointment. Not a happy camper! Can you spell open your mouth pleeeeazzzeeee? hahahaha

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#11
In reply to #10

Re: How to Calculate Reinforce Concrete Foundation

01/27/2011 2:04 PM

CaptMoosie,

We have had fairly cold temperatures here for the most part but today is the third day of a three day warming trend according to our weather man. More snow than usual, but not as bad as S. Dakota. Take a look at the poor guy in the photo clearing his roof in Lead, S. Dak. My roof has between two and three feet of snow on it at the moment. It's melting today, but I understand it will be freezing again tomorrow and another flurry is expected.

We have had several roof collapses in our area reported in the paper. Reporters say they collapsed due to excessive amounts of snow. Could be, or perhaps something wrong with their design or construction. Maybe it would be wise to bump our roof design loading by 10 psf and at least avoid the collapses.

Lots of folk are clearing snow from their roofs, at least around the edge to minimize ice damming. My grandkids have offered to come over this weekend and clear mine, but I'm a bit leary...don't want them falling off the roof onto the driveway.

All the best.

__________________
Bruce
Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#12
In reply to #11

Re: How to Calculate Reinforce Concrete Foundation

01/27/2011 4:51 PM

Hey there ba!

Wowsers, that a hell of a lot of snow on that poor guys roof! I'd estimate it to be around 5 foot depth (unless the guy is over 6 foot tall! LOL).

2 or 3 feet of snow on your roof? Man that's a whole lot of White Stuff! I hope you have a nice steep slippery roof and it slides off soon! hehehe

Around here the Design Load per the NYS Building Code is 45 psf, but they allow a LL reduction per the ASCE-7 Standard. I'm not of the opinion that live load reductions should be allowed for snow and ice loads and have pushed unsuccessfully through our local ASCE Chapter to have the Code reviewed and modified accordingly. I would also like to see an additional 10 psf added to the NYS Snow Load Maps included in the ASCE-7 Standard and the New York State Building Code. I'm not a firm believer in some of this statistical non-sense regarding some parts of the snow maps and feel that what's on the map is sort of on the light side for the most part. I think there has been undue influences involved in the determination of the lighter-than-should-be published snow loads, more due to the construction industry in whole (developers mostly), PAC influences, and politics as usual....the 'ole mighty bucks speaks volumes here in NYS, especially in the Capital, Albany. I think you get my drift (no pun intended).

I've seen enough (and investigated) roof collapses in my day, especially fabricated wood roof trusses. Sometimes it's a steel framed warehouse, usually a pre-fabbed steel building, where I think they fudge factor as well the design to lighten it up on the material side and the engineering signing off on the design (usually a newbie or under qualified, most often a moonlighter) has missed some mistake or not thoroughly reviewed the design. Most often than not it's the actual design of Truss Plate fabricated wood trusses under-designed by the lumber companies designer double-dipping by first taking the snow LL reduction and then later bumping up the allowable LL bending and shear stresses by the allowed 15%! How's that grab you? Nifty way to save $$$$ on materials and labor!!! I usually check it when reviewing the Computer design printouts made by some guy doing it at the local lumber yard, who really is a trained monkey at the keyboards. My design check uses the Truss Plate Institute Standards and Guidelines, so I know it isn't me fudging the design! I always double or triple check my review numbers. The thing that gets me is that some NYS PE (usually Civil) is supposedly reviewing the design and stamping the shop drawings! Most of these guys are New York State Gov't employees moonlighting to make a quick cheap buck, or they're guys working in a Consulting firm moonlighting too! I swear that they don't know what the hell they're doing and haven't a clue how to actually perform a thorough structural design review Most of time they're not carrying any form of Professional Engineering insurance whatsoever, let alone Errors and Omissions coverage! I've provided Expert Witness testimony in a civil court of law on the behalf of affected homeowners that had roof collapses 11 times so far in my career (nearly 34 years in the Biz)....and I hate having to testify because I really dislike attorneys trying to put words in my mouth on cross-examination. Actually, come to think about it, I really really HATE shyster lawyers in particular....damn mouthpieces. Anyhow, most of these homeowners now own the offending PE's home, his savings accounts, his worldly possessions and a goody amount of his income + a sizable settlement with the lumber company and the house builder. Ziiinnggggg poppppp bangggg goes the building! Truly scary isn't it the ineptitude going around? [I like to think that I did the hard knocks early on in my career working for some of the best PE's that I've ever encountered, mainly in small consulting firms where you get a great across the board hands-on approach...not some huge office where you're pigeon-holed for a decade in each position and basically only know a few things and little else!]

the other times the collapses are the result of faulty construction, with most the result of inadequate lateral bracing of the wood trusses. Other causes have been cheaply constructed bearing walls w/ very little in the regard of having enough wall studs in place or spaced too widely, mainly in an effort again to cut down on materials and labor overhead and maximizing profit. In my opinion most building inspectors don't know proper or improper structural design and construction if it bit 'em on the arse! Yes, good at plumbing and electrical and architectural features, but not structural adequacy!

Got go lay down a while as I just got back from the Dentist....ohhh my aching mouth! ***BILL THE CAT ACCKKKKKK ACKKKKK!!!!***

CYA later, and please keep warm up there in the Great White North!!! I don't want to hear that they found you frozen in some snowbank or inside the piled up roof snow that slide down and buried ya, okay? Just ribbing ya! Ahhhhh shades of Second City TV, eh? LOL Loved that show....they sure don't make 'em like the used to!

===Captmoosie signing out Hoser! LOL

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply Off Topic (Score 5)
Reply to Forum Thread 12 comments