Voltage Drop Calculation for Single Phase

01/26/2011 10:16 PM

Voltage Drop = 2*I*(RcosΦ + XsinΦ)*L

Please Explain this formula... How the Impedance is calculated as

Z= RcosΦ + XsinΦ

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Voltage Drop Calculation for single Phase

01/26/2011 10:49 PM

The formulae are:

R = Z * Cos Φ

X = Z * Sin Φ

Therefore Z can only be equal to R÷Cos Φ and X÷Sin Φ

which are obvious from your impedance triangle also.

So, there is something wrong with the formulae you are quoting. Where did you come across them?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#2
In reply to #1

Re: Voltage Drop Calculation for single Phase

01/26/2011 11:19 PM

General Voltage Drop Formula is V= I*Z

and Voltage drop formula used for Single phase calculation is V = 2*I*(RCosΦ+XSinΦ)*L

L is Length

RCosΦ+XSinΦ must be impedance..... Am i rit???? or is there any mistake in my observation

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Voltage Drop Calculation for single Phase

01/26/2011 11:30 PM

Welcome to CR4 bvishnukumar89 (somehow your id has reverted to Guest, please mail Admin)

V = I*Z is applicable to all loads, single phase too. i am unable to understand the other formula you quote. Doesn't look right.

If L = Length, then the Resistance of a conductor = ρ * L ÷ A where ρ is resistivity and A is cross-sectional area.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#4
In reply to #3

Re: Voltage Drop Calculation for single Phase

01/26/2011 11:38 PM

no the actual impedance there is refered as impedance per KM so L factor is used

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Voltage Drop Calculation for single Phase

01/27/2011 12:32 AM

OOPs.

R*CosΦ= Z*{CosΦ}2 and X*SinΦ = Z*{sinΦ}2, therefore,

R*CosΦ+X*SinΦ= Z*(SinΦ2+CosΦ2) = Z*1 = Z

Nothing electrical about this

Your complex looking formula is nothing but V = I * Z after all.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: Voltage Drop Calculation for single Phase

01/27/2011 6:14 AM
  1. KVSRIDHAR has given you the algebra.
  2. If you prefer geometry, draw a perpendicular (to the Z side of the triangle) to the corner which is the join of the R and X sides.
  3. The length from the corner with Φ in it to that point where new perpendicular cuts Z is RcosΦ. N.B. The new triangle has a right angle where perpendicular cuts Z, that being the meaning and purpose of a perpendicular.
  4. The length from corner at other end of Z to the new perpendicular is XsinΦ.
  5. Their sum is length Z = RcosΦ + XsinΦ.
  6. N.B. The angles where the new perpendicular splits the right angle (90 degrees) at the RX corner are 90 -Φ and Φ. A "right angle" triangle has 3 angles which sum to 180 degrees.
Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Voltage Drop Calculation for single Phase

01/27/2011 8:08 AM

Good one. GA to you.

A small modification perhaps to #6?

in all Δs, the three angles total 180°. In a right-triangle, the two angles other than the right-angle therefore total 90°

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: Voltage Drop Calculation for single Phase

01/27/2011 8:27 AM

kvsridhar writing that there was something "not right" about your formula set me thinking....

  1. He was right - the formula supposes that you can get R and X values for each leg of the loop of cable (run length L) which comprises parallel "go" and "return"conductors, each L long - then multiply by 2 for the loop voltage drop.
  2. National standards for wiring give the volt drops per amp per metre RUN at 50 Hz say, for the very good reason that the loop inductance of two parallel conductors depends very much on their diameter and centre to centre distance. For three phase, symmetry is important, else one gets unequal inductances in each phase. When runs are kilometres, at high current, this can cause trouble due to unbalanced voltage and current.
  3. Halving the values for a loop, as if inductance can be isolated [without considering the magnetic field of the return circuit] for one conductor,then doubling the value for a loop is not sound thinking.
  4. Even with direct current, the effect of the magnetic field of the return conductor is not zero, though negligible.
  5. If the formula you gave was from an educational course, please feel free to criticise your teachers for encouraging wrong thinking. Point it out to them!
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Voltage Drop Calculation for single Phase

01/27/2011 8:44 AM

My uneasiness arose from (a) inductance would depend on the coupling, for example the non-inductive shunt in the local test lab is created by winding the two parts in opposition so that the inductance cancels itself. Or the cable may not be a straight run, may get coiled somewhere.

and (b) capacitance would depend on the dielectric, the proximity of the conductors etc..

Anyway, i never had to worry about this in my career, so i am no expert for sure

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10
In reply to #9

Re: Voltage Drop Calculation for single Phase

01/27/2011 10:57 AM

Thanks for the correction on the angles and the good diagrams. You may not have had to deal with power cabling much, but your fundamental knowledge obviously alerts you when there is a source of error!

I wish you a good day.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #10

Re: Voltage Drop Calculation for single Phase

01/27/2011 11:37 AM

Thanks, you made my day ! (night actually in India, but why quibble)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#12

Re: Voltage Drop Calculation for Single Phase

01/27/2011 8:20 PM

For the voltage drop formula, see the section 9.4.3.1 (Voltage drop in short cables), page 210 of the 'Handbook of Electrical Engineering For Practitioners in the Oil, Gas and Petrochemical Industry' by Alan L. Sheldrake. In Figure 9.1, the voltage drop is AC = AB + BC = IR cosØ + IX sinØ = I x (R cosØ + X sinØ).

For single phase, the total voltage drop is 2 times because of the return path and for three phase, it is multiplied by √3.

Single phase voltage drop: 2 x I x (R cosØ + X sinØ) x L

For three phase voltage drop: 1.732 x I x (Rcos Ø + X sinØ) x L

Where,

I - Current through the conductor

R - Resistance (in ohm) of the conductor per KM (or 1000 feet)

L - Length of conductor in KM (or 1000 feet)

X - Reactance (in ohm) of the conductor per KM (or 1000 feet)

Ø – Load power factor angle

Reference thread:

http://cr4.globalspec.com/thread/51446/voltage-drop

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#13
In reply to #12

Re: Voltage Drop Calculation for Single Phase

01/27/2011 11:31 PM

A GA as usual msamad, excellent link, thanks.

Hope to get a little more knowledge from you on this.

1. Why is the expression (R*Cosφ+X*Sinφ) used in place of Z ?

2. Is X only XL or XC or a combination of both ?

3. What do cable manufacturers give in their catalogues ... L and C per some length ?

Would appreciate if you could clarify, thanks.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#14
In reply to #13

Re: Voltage Drop Calculation for Single Phase

01/28/2011 5:45 PM

See the answers below:

1. Why is the expression (R*Cosφ+X*Sinφ) used in place of Z ?

(R cosφ + X sinφ) is used for the simplification of the calculation. The complex value of Z can be also used, such as Z x I = (R + jXL) x I<cos-1φ but this requires to do the phasor calculation (rectangular/polar). In both cases, the end result will be same (see the example in question 2).

2. Is X only XL or XC or a combination of both ?

Ideally, X should be XL - XC but XC value is generally not considered for voltage drop for short run of the cable (since XC is used with negative, its omission is a conservative approach for voltage drop calculation). Since the XL value is also much smaller compared to R value, in many cases, the voltage drop is calculated multiplying only the R value and current magnitude (R x I). In fact, the value R x I is greater than the value obtained from I x (R cosφ + X sinφ). So, voltage drop obtained from simply R x I value is also a conservative consideration.

Example: Assume R = 0.2 ohm, XL = 0.03 ohm, I = 100 A, pf (cosφ ) = 0.8 (lag), φ = 36.87º, sinφ = 0.6

(a) Neglecting XL, R x I = 0.2 x 100 = 20 V

(b) Considering XL, I x (R cosφ + X sinφ) = 100 x (0.2 x 0.8 + 0.03 x 0.6) = 17.8 V

(c) Using Z, Z x I = (R + jXL) x I<cos-1φ = (0.2 + j0.03) x 100 <-36.87 = 0.202<8.53 x 100 <-36.37 = 20.2 <-27.84 = 17.8 – j9.4

3. What do cable manufacturers give in their catalogues ... L and C per some length?

Most of the cases, the manufacturers provide R and XL value for 1000 feet or KM in their catalog (see this cable catalog: http://www.amercable.com/) but, if not specified, they can be obtained from the manufacturers on request. The standard values are also specified in electrical standards. For example, NEC table 8 and 9 specify the R and XL values.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#15
In reply to #14

Re: Voltage Drop Calculation for Single Phase

01/28/2011 9:04 PM

Thank you very much.

This is what CR4 is all about, i have gained unexpected knowledge from what started as an innocous thread by someone else. May your tribe increase, 67model and msamad !

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#16
In reply to #15

Re: Voltage Drop Calculation for Single Phase

01/28/2011 9:51 PM

Yes Mr. Sridhar, I always say I learned more from CR4 than what I contributed. It is a great engineering forum for learning from lot of talented people across the world.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Reply to Forum Thread 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (3); Anonymous Poster (2); kvsridhar (8); msamad (3)