Earthing Questions

01/27/2011 3:52 AM

why two body earthing & two neutral earthing will be done for transformers?

what is the ELCB setting for a 1000 kva Transformer?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: earthing

01/27/2011 5:22 AM

<...why two body earthing & two neutral earthing will be done for transformers?...>

1. So that the circuit protective devices can operate to disconnect any fault, thereby protecting the equipment, the cabling and the personnel working near them.

2. So that the continuity in each connection can be checked by opening one of them and measuring ohms across the gap without risk to the operative, before re-closing them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Earthing Questions

01/27/2011 8:44 AM

i) Logically one each will do; but, as earthing is a critical issue, one doesn't want to take a chance and hence two are provided, just in case one fails. The probability of both failing are very remote.

ii) ELCB setting has nothing to do with the i European practice is 10mA.