Cable Sizing Formula

01/27/2011 4:24 AM

Dear Electrical Friends,

Would like to know the formula to be used for the cable sizing for DOL motors and Star-Delta Motors.

Thanks and warm regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Guest

01/27/2011 4:28 AM

Cable ampacity ≥ 1.25 x FLC of motor, regardless of starting method; plus other corrections that may need to be applied for voltage drop, cable bundling, ambient temperature, etc. It is not so much a calculation as several table look-ups with a decision tree.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3
In reply to #1

Re: Guest

01/28/2011 5:49 AM

But the rating of protective size(fuse/mcb/mccb) will be different.

__________________
pnaban
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Guest

01/27/2011 5:19 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 3 comments
Copy to Clipboard

Users who posted comments:

pnaban (1); PWSlack (1); Tornado (1)

Previous in Forum: Earthing Questions   Next in Forum: UPS Manual Bypass Switch
You might be interested in: DC Motors, Stepper Motors, AC Motors

Advertisement