Generator Slab

01/28/2011 2:10 PM

I have been asked to pour a slab for a Detroit Diesel 12v 149TIB 1100kw generator. This is a fully enclosed, complete unit and the dimensions are 242" long by 118" wide. the total weight is 33,000 lbs. I was thinking of pouring a 6" slab with #5 bar 12" on center, both ways. this unit sits on two beams going the 242" way. Do you think this will be enough?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#1

Re: Generator slab

01/28/2011 2:36 PM

You need an experienced structural engineer.

Where are the bearing points on the deck?

Is the strength of the beams sufficient? If yes, how do you know that?

What are the starting and braking torques?

Will there be a sympathetic vibration problem?

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#2

Re: Generator slab

01/28/2011 2:47 PM

I think 6" will be light for this unit. We installed a 750Kw, 10V @ 25,500Lbs this past fall. The manufacturer recommended a 10" steel reinforced pad. The clients project engineer demanded a 12" steel reinforced pad. The client's project engineer won,

Probably best to check the factory documents that were shipped with the unit. Most have a section outlining pad and installation requirements.

If you don't have factory docs call or e-mail tech support at Detroit. They will be more than happy to help you with this.

Good Luck

__________________
The first 5 days after a weekend are always the hardest................................
Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#3

Re: Generator Slab

01/29/2011 11:54 PM

Hello Guest,

I just ran some quick calculations.

First, if you strictly used the GenSet dimensions, that equals 198.31 square feet. With a deal load of 33,000 pounds that equates into a 166.4 PSF bearing pressure from the generator alone. If you add the slab weight that brings the soil bearing pressure to at least 241.4 PSF.

For mechanical equipment with rotating or oscillating internal parts like motor, pumps etc I like to add a Impact Factor = 1.33 (conservative) to the equipment dead load. That now brings the total soil bearing pressure to:

qu = [(1.33 * 33,000#)/198.31] + 75 PSF Conc. Wgt. = 296.88 PSF

Since you haven't provided any description of the type of soil and it's condition to us I have no way to determine the Presumptive Soil Bearing Pressure to compare it to the total Soil Bearing Pressure. But I can say this, the SBP of nearly 300 PSF is fairly low compared to most allowable soil bearing pressures, unless of course you're building this slab on clay soil, slity soils, saturated soils, organic soils like Peat, Artic Tundra soils. You haven't told us where you are located either and if winter frost is prevalent in your area. Just make sure you construct the equipment slab on well graded and well drained compacted soils. I'd suggest no less than a 6 inch minimum thickness of clean organically free Run-Of-Bank (ROB) gravel subbase under the slab that is compacted to a minimum 95% Modified Proctor Density. Also, increase the slab planimetric dimensions at least 6-inches all around the equipment case.

As far as rebar goes using a minimum Shrinkage & Temperature steel requirement for the slab:

Min. Ast = 0.0018 * 6 * 12 = 0.1296 Sq. In./Ft. of slab width (say 0.13 Sq. In./Ft. width each way). Therefore, using #4's @ 12"o/c Each Way is more than adequate at 0.20 Sq. In./Ft Width. Of course you may use the #5's instead, which may aid in the concrete shrinkage problems.

You don't need the steel rebar for bearing conditions due to the load soil loading.

I hope this helps you. good luck with the project!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.