Relay Rating

02/01/2011 2:15 PM

Could Coil & Contact rating of a relay be the same Ex:120VAC/DC?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Relay Rating

02/01/2011 2:17 PM

They could be, though they need not. On the shelf here is a 24VDC relay with a 250VAC 5A contact rating, for example. Nearby is a 240VAC relay with a 240VAC 10A contact rating.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Relay Rating

02/01/2011 2:30 PM

No need means, Why we are having same rating for both? What is the use? Ca u tell me about Coil & Contact rating briefly. Important points..

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Relay Rating

02/01/2011 3:59 PM

It's all to do with the mechanical construction of the device. In general terms, the smaller the contacts are dimensionally, the lower the rating. The smaller they are, though, the more of them one can get into any defined volume.

Have a look in the RS catalogue (usual disclaimer) for some examples.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#3

Re: Relay Rating

02/01/2011 3:44 PM

Here's what Wiki has.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply Score 1 for Good Answer
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Relay Rating

02/01/2011 7:15 PM

Coils and contacts on a relay are two completely different things, they really have nothing to do with each other except for being parts of the same device. An analogy would be like asking does the hammer and the nail need to both be steel? Could be, but maybe not.

The Coil is the operating component, the thing that makes it work. A relay is kind of like an amplifier, you energize the coil to close a set of contacts, the contacts are the working components that switch another load, either a different amount of current, a different level of voltage or both. So there is no rule that says the coil cannot be a different voltage than the contacts are switching, in fact most often they are not the same. There is conversely no rule that they cannot be the same either, because like i said, they are only marginally related.

That said, there ARE some difference in the switching issue. Typically contact ratings are different for AC and DC, because DC is harder to switch as the voltage increases.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#6

Re: Relay Rating

02/01/2011 9:58 PM

There was one application where the answer to your question is a resounding YES!!!!

Years ago I was working on some signalling relays with VERY long connections. (Like railway distances) The relays were used to receive and "sharpen" the signal to be relayed further through the system.

These "relays" were located at about the 25% voltage drop distance along the lines.

They were called relays since their purpose in life was to "relay the signal."

__________________
Just an Engineer from the land down under.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Relay Rating

02/02/2011 6:10 AM

Please note that coils are always rated with Volatge & VA and contacts are always rated with current. May be, contact current rating will be given at a certain voltage, say, 5A at 240V AC or 1A at 110V DC, etc.

Register to Reply
Anonymous Poster
#8

Re: Relay Rating

02/02/2011 11:00 PM

contact rating are in Amper! example-10A

The contact voltage =the contact will not arc and you r not allow to use voltage less than 25 V!!

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); electricalexpert65 (1); JRaef (1); Just an Engineer (1); PWSlack (2); RDGRNR (1)

Previous in Forum: Help Required for Determining Elec. Load for Roof De-Icing Cables   Next in Forum: RMU

Advertisement