RMU

02/01/2011 3:13 PM

Hİ , I want to ask you the protection type of a RMU . If a load-break switch with a fuse is used so I guess no need to any extra overcurrent protection except the fuse, is it true? But what if a circuit breaker is used? I couldnt see any relay for overcurrent protection on RMU's Can you help me?

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: RMU

02/01/2011 3:34 PM

Normally a RMU will be fitted with a automatic load break switch. IE if one fuse blows it will trip all 3 phases. Some are fitted with CT's with time-lag fuses across the trip coils. Your best bet is to look at manufacturers web sites.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#2

Re: RMU

02/01/2011 3:46 PM

What do you mean with CT? Current transformer?

__________________
jinxnao
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #2

Re: RMU

02/01/2011 8:06 PM

Yes

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: RMU

02/01/2011 6:09 PM

Check to see if your RMU has overload protection. It would be built in the RTU. If so that will proptect the unit. You need to have protection for the conductor.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#5

Re: RMU

02/01/2011 11:46 PM

In practice a directional over current or a directional power relay (or both) would be required in an RMU.

When the systems are large not only you have to consider the excessive fault currents but also there should be an element of time grading between successive interrupters (time grading of relays).

For reliability of a large system an array of main and backup relays are considered necessary.

For reliability you need to automatically isolate a faulty section or might be you have to install an auto-reclosing.

A circuit breaker is more versatile, load break fuse switch is no match to a CB when it comes to system reliability.

If your's is a small and unimportant scheme might be your thinking is valid but as a rule generally not.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: RMU

02/02/2011 6:08 AM

Because, load-break switches have a limited breaking capacity. If you provide a overcurrent relay and arrange to trip the load-break switch thro this relay, then it may so happen that even for currents beyond the breaking capacity of the LBS, the relay might send a trip signal & thus the LBS would damage (flash-over, etc.). That's why one doesn't want to take a chance & only provides fuses for LBS RMUs. Fuses are fast acting. As rightly said in an earlier reply here, it could so be arranged thro micro-switches, that even when one of the three fuses blows, trip supply thro the fuse-blown-microswitch would go to the LBS trip coil and all the three poles of the LBS would open. But, then, here, the LBS would not be opening the short circuit current which alreday was cleared by the fuse. In the worst case, the other two poles would only break the load current, for which, anyhow, the LBS is deisgned.

If you have a circuit breaker in the RMU, then it is prudent to go for relays.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: RMU

02/02/2011 12:52 PM

there is a TRIP COIL in parallel with the fuse.

When the fuse blows, the CT's will drive the coil that will trip the circuit breaker.

I hope this clarifies the question.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#8

Re: RMU

02/04/2011 12:30 PM

Manufacturer ABB has lot of information on its web, may check it address is abb.com

__________________
When was last time you did something for first time.
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: