Impedance Selection For a Three Winding Transformer

02/01/2011 11:42 PM

Hi,

I am not clear how the impedance value is defined for a three winding transformer. I have to design a three winding transformer whose rating is 66/88/110 MVA, ONAN/ONAF/ONAF, 115KV/11.5KV/11.5KV. The secondary winding is two numbers. One of the secondary winding connects to GTG unit and the other secondary winding connects to STG unit. The split in the rating for different cooling level is as below.

ONANONAF1ONAF2
HV6688110
LV1384860
LV2304050

The tender specification says that the minimum impedance shall be 14%.

Appreciate if i could be advised on how the impedance to be defined. In one of the references the impedance is written as 15%/30% for above three winding transfromer rating. Does that mean the impedance between H-X winding is 15%, H-Y winding is 15% and X-Y winding is 30%. Is this understanding correct?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Impedance Selection For a Three Winding Transformer

02/02/2011 9:18 AM

Yes, your understanding is correct. Typically, a lower impedance is seen on the H to other 2 windings, and a higher number between X & Y. If your spec calls for 14%Z, then the manufacturers will design for 14% H-X and H-Y, and whatever results from this for X-Y. Really, it's the impedance from H to X or Y that matters most, as it will affect available fault current in relation to the grid connection.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Impedance Selection For a Three Winding Transformer

02/02/2011 11:57 PM

For your conceptual clearance; If R1 is the primary winding resistance with leakage reactance XL1 and the secondary winding values R2, XL2 respectively, the secondary impedence is Z2 =R2 + jXt2 and for assessment purpose the secondary impedence will be transfered to the primary side by multiplying with turn ratio N1 / N2

Thus total primary impedence seen from the primary side is a sum of primary impedence and secondary impedence referred to the primary.

Your statement that "One of the secondary winding connects to GTG unit and the other secondary winding connects to STG unit" is incorrect practically the transformer is meant for the load of the auxiliaries related to GTG and STG.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3
In reply to #2

Re: Impedance Selection For a Three Winding Transformer

02/03/2011 11:23 AM

Actually, the OP is probably correct. I have seen generating plants where a 3-winding transformer is used as the GSU (generator step-up) for a Gas Turbine Generator and a Steam Turbine Generator, eliminating the need for two separate GSUs. The auxiliaries associated with each generator are then tapped off that winding's bus.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Participant

Join Date: Feb 2011
Posts: 2
#5
In reply to #3

Re: Impedance Selection For a Three Winding Transformer

02/06/2011 7:18 AM

The auxiliary power for the plant is tapped from GTG bus (11KV) of the GSU ( 3- winding transformer). We do not have any tap from the STG bus. The STG connects to secondary2 of the GSU(3-winding) through a generator breaker. The GTG unit connects to the Secondary1 of the GSU through a generator breaker. But for the GTG circuit at the 11KV side we have a tap off at the 11KV SWGR for the station auxiliary loads(GTG and STG units).

The reason for using the 3-winding GSU for the proposed plant is due to space constraint at the substation side. I have also seen 3-winding transformer in other plant but for application wise this is my first design to implement a 3-winding transformer for the proposed power plant. I was not sure about the impedance selection between Primary and Secondary of the 3-winding transformer and thus request a support from the FORUM. Reply from PeterT helps me for further discussion with the transformer vendor.

Register to Reply
Anonymous Poster
#4

Re: Impedance Selection For a Three Winding Transformer

02/03/2011 2:26 PM

what is the difference b/w ONAF1 and ONAF2 cooling methods?