Motor Differencial CT

02/04/2011 11:40 PM

We have motor differencial protection for motor. For that we have provided specification of Class PS CT (350/1 A) to Motor Vendor & switchboard vendor which is as below,

Motor Vendor:

Rct <= 2 ohm

Vk >= 200 V

Imag = 30ma @ Vk/2

Switchboard vendor:

Rct <= 4 ohm

Vk >= 400 V

Imag = 30ma @ Vk/2

However calculated Vk value is 127.83 V

My doubt is that whether differencial protection work correctly

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Motor Differencial CT

02/04/2011 11:52 PM

???????

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Motor Differencial CT

02/05/2011 12:27 AM

Just get the switchboard vendor to talk to the motor vendor.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#3

Re: Motor Differencial CT

02/05/2011 12:40 AM

Differential protection can be there for a large motor but what Class PS CT has got to do with switchboard vendor?

Did not the switchgear vendor reply to you "HA HA HEE HEE HA HA ... Oops"

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Member

Join Date: Jan 2011
Posts: 8
#4

Re: Motor Differencial CT

02/05/2011 11:49 PM

Hi,

The calculated Vk is 127 then the CT will be sufficient since the Vk rating is 400V.

As for motor differential, so long there is a CT connected to the neutral and the phase, it will work.

Hope this helps

ecsales

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Motor Differencial CT

02/07/2011 10:51 AM

I would like to study the excitation curves of both the CTs before answering. I feel that there could be stability problems. Because going by the date given at 127 V through-fault voltage, the excitation currents of both the CTs would differ and the relay might act.