how to select size of earth electrode
Re: Electrical Earthing
02/05/2011 8:58 AM
Hire a professional.
02/05/2011 10:15 AM
By, "size", do you mean diameter or length?
02/05/2011 2:10 PM
Consult your local code requirements, if any. If not, you still should use a recognized standard such as (US)NEC, BS7671, or others. It also depends on earth conditions.
02/05/2011 11:21 PM
Hi, Guest
Are you refering to ground electrode, if yes
3/8 x 5ft
1/2 x 1oft
5/8 x 10ft
3/4 x 10ft
1 x 10ft
Good Answers: 5
02/06/2011 12:52 AM
The best method is to consult an experienced engineer. If you are a young engineer you should know the prospective fault current,type of soil,type of installation (hone, industry,substation-system earth,telecom earth,lightning earth,surge earth etc)
pnaban
02/06/2011 11:36 PM
Refer IS-3043, clause 10.3 & Section 12.2.2.1.
Tell me if you can't find them. I will help you with the formulae.
02/07/2011 2:29 AM
Can u explain, please
Good Answers: 170
02/07/2011 10:45 AM
I am sorry! Please quote carefully. This section 12.2.2.1 of IS 3043 specifies only the sizing of Protective Conductors and NOT the earth electrode sizing. Earth Electrdoe sizes are given in Section 9 of IS 3043 rather.9.2.1 gives typical plate electrode sizes & 9.2.2 gives typical Pipe or Rod electrode sizes.
Anonymous Poster
02/08/2011 12:11 AM
hI, aLL
i INTENT TO buy this book IS 3043, i live in Dubai where can i get it.