Can CBCT be Used in Restricted Earth Fault?

02/07/2011 8:49 AM

Can we use CBCT for restricted earth fault? In one system CBCT is given for sensing of restricted Earth fault but during the testing found that One CT in Phase side or Neutral side is not enough to drive the relay coil. any suggestion?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Can CBCT be Used in Restricted Earth Fault?

02/07/2011 10:20 AM

But, where have you located the CBCT for sensing the restricted earth fault current?

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: Can CBCT be Used in Restricted Earth Fault?

02/07/2011 5:29 PM

EE65, I've sent you a PM.

__________________
The reports of my death are greatly exaggerated.
Reply
Participant

Join Date: Oct 2010
Posts: 1
#3
In reply to #1

Re: Can CBCT be Used in Restricted Earth Fault?

02/08/2011 2:54 AM

One CBCT is before the breaker in phase side & one CBCT is before the creating the neutral in generator neutral side.

Reply Off Topic (Score 6)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Can CBCT be Used in Restricted Earth Fault?

02/08/2011 6:20 AM

I think that logically the scheme should work. But then, as rightly said by you, the CBCTs wouldn't have the necessary burden rating to drive enough current throug the relay coil, particularly if the relay is of the electro-mechanical type. Have you tried with digital relays?

Reply Off Topic (Score 4)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: Can CBCT be Used in Restricted Earth Fault?

02/08/2011 1:12 PM

I take it that was the reply to my PM

For the benefit of others here's what was in the PM

It's a long time since I had any dealings with REF and the ones I dealt with all had independent phase CT's and with high impedance relays. Now I can see a CBCT being used to detect REF but with what kind of relay?

Geo. Ellison used them for outgoing feeds from their ACB panels but they used normal current relays. (Not that I was too impressed with them, I set fire to 2 ACB's in one afternoon thanks to their poor design)!*

* It was comical I radioed my mechanical counterpart and asked him to re-close one ACB as I was 150' up in the air. Reply came back "you can bu**er off, the sub's full of smoke"!

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: Can CBCT be Used in Restricted Earth Fault?

02/09/2011 5:28 AM

I am sorry! I should have replied your PM. But, I was not sure that you wanted a reply.

Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#7

Re: Can CBCT be Used in Restricted Earth Fault?

02/14/2011 5:54 AM

no.. if u use like that, it will be stand by earth fault protection and not REF. REF will be effective if all the three phase CT secondaries is connected in series and connected with neutral side CT secondary. Moreover most of the REF protection operates with voltage operated coil . so maybe the current you injected while testing would not have produced enough voltage across the relay coil to operate it.

__________________
You don't understand anything until you learn it more than one way.