Gas Tightness & Air Tightness Test

02/07/2011 10:28 PM

hi, while i'm reading a commissioning manual for 210MW boiler, i have come across with gas tightness & air tightness test. But it hasn't provide the sufficient details about where it has to done. I guess it might be in main steam pipe line. Is it right or else please provide sufficient detail. Please give what is the difference between these two tests.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Gas Tightness & Air Tightness Test

02/08/2011 2:44 AM

Contact the publishers of the commissioning manual directly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Feb 2009
Location: BHARUCH , GUJARAT
Posts: 4
#2

Re: Gas Tightness & Air Tightness Test

02/08/2011 10:34 PM

Steam lines are tested hydraulically with water as per code. Gas tightness or air tightness test are tested on boiler & duct side with smoke bomp to ensure that there is no leakages in Boiler wall throgh fins.

Register to Reply
Member

Join Date: Jun 2009
Posts: 6
#3

Re: Gas Tightness & Air Tightness Test

02/08/2011 10:36 PM

Must be for the air and flue gas path......... Anyway, consult the boiler manufacturer.

Register to Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#4

Re: Gas Tightness & Air Tightness Test

02/09/2011 2:37 AM

gas tightness test

It should only and exclusively refer to the tests necessary to prove the integrity and strength of the gas supply pipe to the boiler and not to the boiler flueways, economiser flueways or steam pipe. The context in the manual should have told you this.

If you don't know what it means you are not competent to carry out the test. Get a certified gas engineer in to do the test otherwise you insurance people should have a fit.

air tightness test

This may refer to almost anything including economisers, flueways external to the boiler or if it is a water tube boiler to the combustion chamber etc. Again the context in the manual should help in deciding what is being referred to.

Regards,

Gasman

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#5

Re: Gas Tightness & Air Tightness Test

02/09/2011 7:28 AM

The gas and air tightness is on the fire side, not the steam lines.

But be extremely careful, since this should be done by the manufacturer of the equipment else you could lose the warranties.

Also to perform the air or gas tightness test you need specialized equipment which is cheaper if you get the manufacturer to do the test with their own equipment, plus you have the benefit of getting re certified and warrantied