Do any one know how to calculate cooling tower evaporation rate and what is the standard rate for per tonnage.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cooling Tower

02/08/2011 2:42 AM

Cooling tower manufacturers publish performance charts for their towers.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Cooling Tower

02/08/2011 7:07 AM

To determine evaporative condenser or cooling tower requirements, you must add the the compressor energy to the refrigeration tonnage. There is no one standard multiplier for this, because it depends on the refrigerant, the compression ratio, and the type of compressor. The THR (total heat rejection) at the condenser/tower can run from about 1.15 to 1.40 (very rough numbers) times the refrigeration tonnage.

If you are using Btu as your units, 1 hp = 2545 Btu/h.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Apr 2010
Posts: 22
#3

Re: Cooling Tower

02/13/2011 6:31 AM

The following should be helpful: E = 0.0013 x delta T x Q.

Where E = Evaporation rate in cu.m. /hr

Delta T of the Cooling water in Deg C

Q = Recirculating rate in cu.m./hr.