Choosing Electrical Wire

02/11/2011 4:07 PM

Greetings All,

I'm building a small 1.1 MW solar farm and my engineer has asked me to make a choice on wire.

We are in the desert, the wire will be buried in conduit unless we go with direct bury.

He says to choose between 350 MCM Cu or 600 MCM Al, it has become a significant financial decision in the last year since the price of Cu has gone up.

I was hoping some of you experts could give me an approximate price per foot of each off the top of your head since everybody I have asked for quote wont get back to me until next week and i was hoping to give him an answer so he could finish over the weekend.

Also Ya'all wouldn't happen to know the price difference between 600 MCM Al direct bury and regular THHN?

Also any personal opinions you would have on making this choice would be appreciated.

Thanks

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#1

Re: Choosing Electrical wire

02/11/2011 4:48 PM

"Also Ya'all wouldnt happen to know ..."

Isn't a ya'all a two-masted sailing craft similar to a sloop or cutter?

[edit] My mistake. You all is the company that rents out those little orange and black trailers by the day, week or month.

I've been waiting for two years to use that one!

__________________
Semper Ubi Sub Ubi
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #1

Re: Choosing Electrical wire

02/11/2011 6:41 PM

Whatever are yawl talkin' 'bout?

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Choosing Electrical wire

02/11/2011 5:48 PM

What voltage does your farm generate?

Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#9
In reply to #2

Re: Choosing Electrical wire

02/12/2011 2:06 AM

The inverters are 260 kW at 480v, so 480v

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Choosing Electrical wire

02/11/2011 7:09 PM

From NEC Table 316-10, 350MCM copper is most closely equivalent to 500MCM aluminum. The cost difference pales into insignificance when compared to a 1MW solar farm and its appurtenances. It ought to take only a 5-minute phone call to get local/regional comparative prices, anyway.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#10
In reply to #4

Re: Choosing Electrical wire

02/12/2011 2:08 AM

You would think it would be that easy but after 4 hours I come on bended knee to you guys.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: Choosing Electrical wire

02/11/2011 9:24 PM

Without knowing a lot more about the configuration of this solar farm I could not give you a true knowledgeable opinion. With limited knowledge though I would recommend the copper instead of aluminum. If just for the thermal expansion problem that aluminum has when it heats up. This is why when thinner gauge aluminum wire was used to wire people's homes, the self heated aluminum would expand farther than the hardware anticipating a copper wire expansion. This then caused many loose wire connection that would occasionally through a spark that would ignite something. Most junction hardware today have been redesigned to accept both types of conductors. So it is possible to fabricate your whole facility safely using either wire. But with wire cost likely being a small part of the whole expense and there being a small but real possibility that aluminum could add a hidden problem to this project, I'd choose copper.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#11
In reply to #5

Re: Choosing Electrical wire

02/12/2011 2:19 AM

I have been able to get some ball park figures off the internet, yes, relibility is a question, but the average is about $7/Lft for 350 MCM Cu and $2.25/Lft for 600 MCM Al. After a few thousand feet the difference adds up and cannot be ignored. Solar farms are not Gold Mines, and if it isnt financially profitable it isnt feasible.

Now the question is cost of direct bury as opposed to using conduit.

The inverter companies say Al is ok with them as they are using compression couplings.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Choosing Electrical wire

02/11/2011 10:15 PM

$164 per liner foot, will ship next day on receipt of your credit card details.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 2 for Off Topic
Anonymous Poster
#7

Re: Choosing Electrical wire

02/11/2011 10:58 PM

Worse, Redfred. The aluminum to copper (or other metal) mechanical connector was never solved for any significant current. The solution for high voltage aluminum cable you see on high voltage towers is a special one, but here it is: a cold weld crimp end on alu, a copper flat bar for termination. The economics on this is for hundreds or more miles. By the time you are done with this for your purpose, copper cable will appear cheap in comparison.!

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: Choosing Electrical wire

02/11/2011 11:14 PM

I think that you ultimately agreed with me that copper is the preferred metal conductor. I thought that there were some spring loaded junctions that were designed to compensate for the expansion. You are likely correct though that these special junctions will quickly eat away any savings one might get from using aluminum. All savings will quickly evaporate when a non-aluminum grade junction gets used on aluminum and ignition occurs.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#13
In reply to #8

Re: Choosing Electrical wire

02/12/2011 2:30 AM

The special connectors are not that much more than the regular connectors, and most of the equipment in the solar biz is rated for Al already anyway, its the 5 dollars a linear foot difference that is significant.

So no one has any idea of the cost of 600 MCM Al THHN as oposed to direct bury 600 MCM Al, per linear foot?

Dudes???

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#12
In reply to #7

Re: Choosing Electrical wire

02/12/2011 2:22 AM

Copper has really gone up in price lately.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#15
In reply to #12

Re: Choosing Electrical wire

02/12/2011 10:48 AM

So has Al. $1.00USD per pound for Al cans.

Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#14

Re: Choosing Electrical wire

02/12/2011 9:06 AM

I would get a new engineer.

This is a design issue. The answer is dependent on the price of the acceptable conductors. Surely this is not a DIY project. You are talking about a very significant line item. The approved drawings will need to call the conductor. Would you really ask a customer to pick a conductor? I could go on and on.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#16
In reply to #14

Re: Choosing Electrical wire

02/12/2011 12:10 PM

Guys, the recomendations for using Al wire are coming from nationally recognized Electrical contracting firms with their own engineers, I always get more than one opinion.

Critisizing someone or firm, you know nothing about is low class and not up to the standards of CR4.

No its not DIY, I hire professionals, and manage construction myself cause giving the managment over to an EPC adds 20% to the cost and its just not in the budget.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#17
In reply to #16

Re: Choosing Electrical wire

02/12/2011 6:19 PM

I'm sure you are going to get it figured out. You said a small 1.1 MW PV facility in the desert. This is not small. You may have the expertise to engineer this wire run, your question implies that you do not. As for the engineer I was referring to, it is you. That was a little harsh, sorry. Maybe I've got it all wrong and jumped to the conclusion that asking that question on the CR4 forum without any details, and expecting an expert to spit out the answer was unrealistic.

Are you building these inverters, or purchasing them? If you are purchasing them I have found very extensive engineering resources available with your purchase. (Solectria, Satcon) are two I deal with. They will answer your questions. Good luck.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#18
In reply to #17

Re: Choosing Electrical wire

02/12/2011 7:52 PM

Im an old broke home developer that got suck with some property. In the commercial solar business 1.1 Mw is considered small, in fact anything under 20 Mw is the small catagory for the CPUC, CEC, NREL, etc. Im an organzer, (developer), I do not have the expertise to engineer this, so I hire engineers and consultants, etc. I then double check their answers cause Electrical engineering is not my area of expertise. Sometimes i get a third opinion from CR4, sometimes they give good answers and sometimes the court jesters come out and they dont have a clue.

The suggestion for Al conductors came from a nationally known EPC that is considering partnering with me. (Engineering-Procurement & Construction firm)

I thought the CR4 "experts" opinion on the cost of wire was straight forward, surely one of you guys knows how much 600 MCM Al THHN wire costs a Lft as opposed to the cost of 600 mcm direct bury.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Anonymous Poster
#19
In reply to #18

Re: Choosing Electrical wire

02/12/2011 8:31 PM

For one thing, prices are quintessentially regional/local, so overseas CR4 members are not likely to have any idea at all of prices around Mojave. For another, CR4 is somewhat more about technical discussion than about economics. If I wanted to know the price of something, CR4 would be among the last places I would ask.

I cannot see at all why you are unable to get at least budgetary prices from nearby suppliers within hours, if not minutes. Is service in California really that bad?

ξ

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#20
In reply to #19

Re: Choosing Electrical wire

02/12/2011 9:23 PM

I agree. If the only thing that Spacecannon wants is a price, then CR4 is the wrong place to come for just a price. Now once he's found the variety of prices one can find for various copper and aluminum wires I would understand asking us here what advantages each type provides so that an informed evaluation of each price can be weighed. But frankly asking us just for a price is rather insulting.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#23
In reply to #20

Re: Choosing Electrical wire

02/12/2011 9:35 PM

Redfred,

Seriously, if you work with it and dont have any idea on the costs, then you have no business engineering anything with it, I expect an Electrical Engineer would have a clue.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#34
In reply to #23

Re: Choosing Electrical wire

02/13/2011 8:13 AM

Then you have no idea what an electrical engineer does. A contractor electrician would have an idea of what the wire cable costs. How many threads have you seen here where price quotes were included in the discussions, none that I remember.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#35
In reply to #34

Re: Choosing Electrical wire

02/13/2011 11:54 AM

Redfred,

I disagree with you, you think only engineers occupy these spaces? If an engineer doesn't have a clue about the cost of materials the "he" doesn't care about his clients, a wildly arrogant position. Everything, EVERYTHING, has to be taken into account when engineering a system, structure or facility. I have seen people ask about prices on things here, why not! Your argument is a fallacy and doesn't hold water.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#36
In reply to #35

Re: Choosing Electrical wire

02/13/2011 1:22 PM

You seem to be refusing to see anything but your own little problem. So sad.

Yes, any engineer has to work within their budget on a project. An engineer on that project has access to all of the relevant parts and concerns of that project so they can make a sound judgement on where to wisely spend the money to produce a functioning product with an acceptable lifetime. As you've said, "Everything, EVERYTHING, has to be taken into account when engineering a system, structure or facility." When I earlier gave you my opinion that I preferred copper over aluminum I also pointed out that there was not enough information to say which conductor is worth the money. I did try to inform you about a hidden hazard that one finds when using aluminum conductors. Others here have also agreed with me that there are hidden problems that one can find from using aluminum wire. Instead of trying to use my information or granting us more information to help you make an informed choice you just ask for a price quote. Well look at the words in that red bar on the top of the page. They say "The Engineer's Place for News and Discussion®" This space is for Engineers and those who wish to discuss things relevant to Engineering. If you want a price quote, ask a vendor that will take your money.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#37
In reply to #36

Re: Choosing Electrical wire

02/13/2011 2:35 PM

Redfred,

You seem to be unable to see anything beyond your own arrogance which is a big problem for you. Alot of people gave opinions on use which is good and on topic. Your problem is you cant stay on topic, too big headed to keep things simple, you come off as a blow hard. NOT SAD, PATHETIC. You act like a Doctor who prescribes medicine to patients and doesn't have a clue about those costs, when he could prescribe a generic, the good ones have a clue, not exact, but a range. The arrogant ones blow you off.

I REST MY CASE!

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#22
In reply to #19

Re: Choosing Electrical wire

02/12/2011 9:32 PM

Give it a break with the criticisms, It was late on Friday and most shops don't deal in 600 MCM Al.

Of course I wouldn't consider prices from out side of US Valid. Inside US would be close enough for comparison.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#21

Re: Choosing Electrical wire

02/12/2011 9:26 PM

Well first off, there is a lot of really good info from my fellow CR4 guys here. THHN 350MCM Cu is good for 350 Amps, Al 250 Amps if using THHN insul. What are your runs, 1.1M you will need to parallel many Cond/Ph. 500MCM THHN is good for 430 Amps, you will need to parallel many cond/Ph. I personally do not like Al and refuse to use it regardless of the upfront expense. Al has too many losses and should have never in my book been used as an electrical conductor, but this is a personal issue.

You never gave us how many feet your runs are. If you did I missed it. The other question is , are you in need of this wire from the panels to the inverters, or from the inverters to the power distribution? Where does the Utility fit in with this? Are you qualified to deal with this power? And why would your engineer be asking you, what wire you want to use? He should be specifying what wire is needed for the application. Hands down. I would question your engineer and check his qualifications. If this is going to be tied into the grid, I am sure the utility will be all over this, or should be. I deal with them all the time, they are always double checking with their engineers on everything I do. And that is a good thing in my book. Safety First, always.

__________________
"Real Bass Players" do not use picks
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#24
In reply to #21

Re: Choosing Electrical wire

02/12/2011 9:47 PM

Im not asking anyone's opinion on the size of wire to use for my runs. The ELECTRICAL engineer made the specifications, then I had them doublechecked. All that was asked of me was which type I wanted to use Cu at 350 MCM or Al at 600 MCM, so I looked into prices and maintence considerations and drawbacks.

All Im asking of the freindly helpful gentlemen of CR4 is an opinion on price and then I asked for any feedback on the Use of Al. Thanks for your Opinions and Help, NOT!

What happened to CR4, I didnt ask about color or shape but ya'all seem to think its relevent.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply Off Topic (Score 6)
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#27
In reply to #24

Re: Choosing Electrical wire

02/12/2011 10:11 PM

My recomendation is to us Cu only, 500MCM min in my opinion, I paid $7.35/ft 4 weeks ago, copper is up and down, when I purchased it 2000FT, I was on the phone and email several times a day as it fluctuates every 2 hours. I waited till it dropped to 7.35, it was on the initial inquiry 9.80/FT. I would not use Al for any thing but to make cans with. It should not be used in electrical installations, but then this is my personal opinion. Also the questions are related to runs and multi conductors per phase. Amp ratings, you are talking 1.1MW. 480 3Ph. You may even consider using 1000MCM THHN depending on your voltage drop/distance of cable to reduce the amount of multi conductors. As for price, this is like water. It is in constant flux.

Find several suppliers in your area, the larger suppliers can get better price breaks,

I use 6 different suppliers for products. Each has their specified expertise they deal with and each has better pricing depending on what they deal with. On the 500MCM I was quoted as high as 11.85/ft for 2000FT on the same day I was quoted 7.35 so you know who got the purchase order, and the quote was only good for 4 hours. After that it would have to be re-quoted.

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#29
In reply to #27

Re: Choosing Electrical wire

02/13/2011 12:11 AM

Jimh77,

GA, and thanks for your opinion.

Idont know how this got marked off topic, and so fast must be a glitch, I'll have to report it to Admin.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#32
In reply to #29

Re: Choosing Electrical wire

02/13/2011 1:34 AM

I marked it to be "off topic" This was to be btwn us afrere your blasting and rightly so. I think I was a bit hard on you with so little info given to work with. It's a bit tough to work on issues when not enough info is given at first which is one reson I was maybe some out of kilter in my response to you in the beginning. The big issue is in pricing. It's impossible to give a price. To many variables with copper. I seriously am against AL wire. But, it is very personal why I feel this way. It is mostly residential, but I carry this in industrial/commercial also. I hate aluminum wire. As I said, it is very personal and I refuse to use it.

__________________
"Real Bass Players" do not use picks
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#33
In reply to #32

Re: Choosing Electrical wire

02/13/2011 2:33 AM

An honest opinion without criticism, is a good answer.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#38
In reply to #24

Re: Choosing Electrical wire

02/13/2011 5:03 PM

350 CU does not equate to 600AL so where are you getting your cable sizing from?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#39
In reply to #38

Re: Choosing Electrical wire

02/13/2011 5:27 PM

I know, the engineer wants so oversize it cause of the desert heat. Im getting it from my engineer but anyone can look up equivalents on the web.

In the picture, nice box, what kind of facility uses it and what for?

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#44
In reply to #39

Re: Choosing Electrical wire

02/20/2011 6:14 PM

It's a 500KVA transformer 600mmAL singles.

On the subject of engineers over specifying. I had 2 1000KVA transformers to install, he specified 960mmAL two per phase. It was like trying to bend scaffold poles!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#45
In reply to #44

Re: Choosing Electrical wire

02/20/2011 7:10 PM

Wow, ya gotta use bending Irons for that unless your built like the incredible HULK.

thx

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Feb 2011
Location: PHL
Posts: 12
#25

Re: Choosing Electrical wire

02/12/2011 9:56 PM

Greetings to Spacecannon,

Asking personal opinions from your comrades in CR4 is a sign of humility even you know the answers. You recognize the importance of one's contribution, comment which may not be applicable today perhaps tomorrow.

We may not give you any prices for your asking because prices vary from places to places, and current prices changes.

But we can give you alternatives to think about to help you choose the the best and most economical option.

We presumed that you have the right choice in cable sizes, factors were considered like ampacity of cable, derating factors, voltage drop. etc. Now you are to decide whether to use the ff:

  1. 350 MCM Cu vs 600 MCM Al - bury with conduits.
  2. 350 MCM Cu vs 600 MCM Al - direct burial
  3. 600 MCM THHN Al Free Air bury in conduits vs 600 MCM Al direct bury

For #1: Both of the two can be used but prices of cable per linear foot will dictate economy.

For #2: Both of the two can be used but prices of cable per linear foot will dictate economy. There will be reduction in material and labor costs.

For #3: Both of the two can be used but prices of cable per linear foot will dictate economy. Consider the costs of conduit installations.

I opt for #2, whichever cheaper in material and labor costs b/w copper and aluminum will be used.

Hope this can be of help.

____________________

"Iron sharpens Iron"

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#26
In reply to #25

Re: Choosing Electrical wire

02/12/2011 10:01 PM

Electiguru62211,

YOU ARE AN HONORABLE AND GOOD PERSON!!!

GA, Thanks for your opinion

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Active Contributor

Join Date: Feb 2011
Location: PHL
Posts: 12
#30
In reply to #26

Re: Choosing Electrical wire

02/13/2011 12:11 AM

Thanks.

____________________

"Iron sharpens Iron"

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#28

Re: Choosing Electrical wire

02/12/2011 11:15 PM

Out of idle curiosity, where is this proposed installation, and how far is the grid tie-in from any recognizable municipality? Somehow from 480 volts I get a whiff of another Californicated grid folly, probably wrapped up all purty in goobermint subsidies.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#31
In reply to #28

Re: Choosing Electrical wire

02/13/2011 12:20 AM

tornado,

I cannot answer all of your questions because of NDA concerns, but the tie in is at the corner of the lot, the facility is in a city that will use it, No other rebates than the Federal Cash grant everybody else is gettiing, just adapting to survive, dude.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#40

Re: Choosing Electrical wire

02/13/2011 5:39 PM

Just going on past experience 1000KVA transformers had either 7 x 500CU or 7 x 600AL singles.

I've only installed two 750KVA 550V transformers that had a multi cored SWA feeds to the LV board. We used two paralleled 3&½ core 400CU.

350 CU is far too small!

The photo is a "baby" 500KVA trany! 4 x 600AL

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#41
In reply to #40

Re: Choosing Electrical wire

02/13/2011 8:41 PM

cool picture, thanks.

I dont know if 350Cu is too small, all his stuff gets double checked by the EPC and then tripple checked by the Utility Co. , so if he screws up, he has to fix it, and it makes him look bad.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#42
In reply to #40

Re: Choosing Electrical wire

02/13/2011 9:07 PM

This 1.1 MVA system is subdivided into four parts, each 276 KVA as I recall....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Feb 2009
Location: Mojave Desert, Southern California
Posts: 515
Good Answers: 13
#43
In reply to #42

Re: Choosing Electrical wire

02/13/2011 9:26 PM

Technically its 5 parcells with a small remainder, 4 260 inverters and 2 small 30s, the 1.1Mw is DC.

__________________
The person who wrote the above is not resposible for spelling, grammar or puncuation, ......
Register to Reply
Register to Reply 45 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Doorman (1); electlguru6211 (2); Jimh77 (3); lyn (2); PFR (2); redfred (5); spacecannon (20); TonyS (4); Tornado (3); wareagle (1)

Previous in Forum: Lightning Rod Usage   Next in Forum: 220V Psc Motor Converted To 110V?

Advertisement