450Ton Carrier Centrifugal Chiller

02/11/2011 10:27 PM

I need to explain that when the chiller shuts down and the chill water pump keeps running is better for the chiller operation as against when the the chiller and the chilled water pump shuts down simultaneously.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: 450ton carrier centrifugal chiller

02/11/2011 10:55 PM

wot on erth R U talkin bout?

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: 450ton carrier centrifugal chiller

02/12/2011 12:02 AM

If there is no water flow, the refrigerant side of the chiller will continue to pump down, possibly freezing the stagnant water in the chiller. (It depends on the relative sizes of system parts, so this may or may not happen.)

Whoever does not understand this needs to explain to you, not you to them.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#4
In reply to #2

Re: 450ton carrier centrifugal chiller

02/12/2011 10:49 AM

GA TORNADO and a good explanation of the most important characteristic to consider. I would also add that a 450ton unit has enough of a piping system attached, that just from an operating point..... I would much prefer to bypass some chilled water at the decks, or vav, or whatever exchangers ... than to start and stop water flow, thereby picking up a lot of sediments and redistributing them in the valve passages.

__________________
klearzen
Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9
In reply to #4

Re: 450ton carrier centrifugal chiller

02/13/2011 10:23 AM

What sediments are you talking about?? Have you ever worked on a chiller in your entire life? If you did, does it still run after you got your hands on it?

Reply
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#11
In reply to #9

Re: 450ton carrier centrifugal chiller

02/13/2011 10:58 AM

Dear Fedski, Welcome my Polish friend. You have asked some ridiculous questions, but in all fairness you have sparked me to ask myself, why I seek anonymity here(klearzen). My reasoning....A throwback to days gone by when, in the wild west of the internet, you really could be anyone you wanted to be. Who am I ? I am turning 50 years old this month... have been a sailor, a contractor, and engineer....a father, a brother, and son. I was born here in Saint Louis. My family roots lead back to Ireland and Germany. Who are you FREDSKI? Smiles, Ray

__________________
klearzen
Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#12
In reply to #11

Re: 450ton carrier centrifugal chiller

02/13/2011 11:17 AM

I'm a 30 year HVAC commercial service contractor is So Calif. If you're concerned about sediment, try looking in the strainer.

Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10
In reply to #2

Re: 450ton carrier centrifugal chiller

02/13/2011 10:24 AM

Over 5000 posts? Is this your life, to sit on this blog all day and berate people asking questions?

Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#3

Re: 450ton carrier centrifugal chiller

02/12/2011 6:39 AM

You don't need your pump to stop from running when your air conditioned space are functional or with load.

Your chiller stops and the chilled water pump is running-when the load of the air conditioned space had decreased making the temperature of the incoming chilled water to chiller equal to the preset temperature (stop) of the chiller evaporator. The pump will continue running in order to absorbed the heat of the conditioned space, until such time the preset room temperature is achieved, the pump will stop running.

This is just like the thermostat of a window type air conditioning unit. The compressor stops when a preset temperature is attained-an increase of temperature will make the compressor turn on again, while the fan can not stop, not unless you want to turn all the unit off.

_______________

If you do not know the complex, then get back with the basics

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#5

Re: 450Ton Carrier Centrifugal Chiller

02/12/2011 10:56 PM

450 TR capacity is a big chilling a machine. It has its own control panel and system to operate the chiller based on the settings . You need not and cannot shut down the pump.

Reply
Active Contributor

Join Date: Apr 2010
Posts: 22
#6

Re: 450Ton Carrier Centrifugal Chiller

02/13/2011 2:25 AM

In all air-conditioning applications whether used for comfort or process cooling, the Chiller's Controls are designed to acheive the desired Chilled water temperature set-point, once this is acheived the Chiller is automatically shut down by its Controller, this is called a 'cycling' shutdown. The Chilled water pump has to continue to run to supply the cold water to whatever downstream equipment it supplies to and returns back to the chiller, this is the complete loop or circuit, eventually the water will pick up heat, its temperature will rise beyond a certain range and the Chiller's Controller will re-start the Chiller. This is how the system is set-up, irrespective whether it is a 450 TR Chiller or a 2500TR Chiller.

Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#7

Re: 450Ton Carrier Centrifugal Chiller

02/13/2011 4:19 AM

Hi Guest,

There have been some good answers to your query re the chilled water pump operation with regards to a centrifugal chiller.

On initial startup the chilled water pump is normally operated for a period (say 10 mins) to achieve a mixing of the chilled water in the system so that a representative temperature can be measured to determine whether there is a demand for cooling. If so the chiller is then enabled and the chiller's own control system begins the startup sequence i.e. oil pump and condenser pump before enabling a start of the drive motor.

Cyclng on and off as a function of temperature control

Depending on the system load the chiller may cycle off when the temperature of the chilled water goes beneath setpoint (normally set ± 6ºC) and the chiller will then be held off by the recycle timer (± 20 mins). During this cycling on and off as a function of temperature control the chilled water pump must be kept running in order to supply water to the connected loads plus equalise the pressures within the chiller. The condenser pump and the oil pump will be shut down by the chillers control system during this recycle period.

Once the chillers recycle time has elapsed and if the temperature of the chilled water has risen above set deadband temperature (normally ± 4 to 5ºC above the setpoint) the chiller will go through it's startup sequence and restart.

Shut down of the chiller

When the chiller is required to be shutdown (cooling no longer required) then the chiller control is disabled and the chiller goes into the shutdown sequence i.e. the drive motor is disabled, the load control vanes are closed (sometimes referred to as pre-whirl vanes) and the oil pump and condenser pump time out. The chilled water pump however should be kept operating on a run down timer (delay off timer) for a period of 3 to 5 minutes before switching off. This run down time is to stabilise/equalise the pressures within the chiller (ensuring no risks of freezing during any refrigerant boiloff in the evaporator) and also mix the chilled water in the system to ensure the water is all basically the same temperature.

The manual supplied by Carrier for your chiller should give you a full description of the recommended operation sequences and parameters and I suggest you refer to this manual as well.

The above noted sequences are good practice in the operation of centrifugal chillers but it has been my experience that some people, when using a temperature control system other than that included by the manufacturer, just switch off everything when either cycling or shutting down the chiller. My experience, gained over many years of experience installing, servicing and repairing centrifugal chillers (all makes but especially Carrier), has been that although the chillers are designed to handle a sudden interruption (oil headers to enable lubrication of the impeller gearbox during pump failure etc) this practice increases the risk of damage.

Hope the above info is of assistance in answering your query!

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#8

Re: 450Ton Carrier Centrifugal Chiller

02/13/2011 8:45 AM

The chilled water pump needs to keep feeding the building and or process. When the return water temperature rises above the set point then the chiller will start back up.

This is S.O.P.

Reply
Reply to Forum Thread 12 comments

"Almost" Good Answers: