Differential Protection Tranformer

02/14/2011 2:20 AM

dear sir,

we have 15kv genaretor(GE)240MW and 15\220 transforme we have started for frist syncro with 220kv bus , and we got defferencial protection in theree phase , thaa relay is GE C60T , we did secondary injection throw tha cable end to end from both sides, current and angle and phase rotetion ok , Angel is R= 0 ,Y=-120.B=-240, Anti clock rotetion, and i am wainting for some one sagision , for ther chek points,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Differential Protection Tranformer

02/15/2011 2:44 PM

First of all, the GE C60 is a Breaker protection relay - it doesn't have differential functions. Are you sure this is what you have, or a T60 Transformer protection relay?

Next, what differential function tripped it, instantaneous or percent differential? Did someone qualified develop the relay settings, including harmonic restraint to ride through the inrush, etc.? Did you enter the correct transformer winding phase compensation so that it accounts for the phase angle difference between primary and secondary windings? Are the CTs wired with the correct polarity, per the manufacturer's instructions? Are the correct CT ratios programmed? This are a few of the items that can cause a false trip on a differential relay. You have some investigation to do!

__________________
To get the right answers, first you need to ask the right questions.