How to Measure Earth Resistance?

02/14/2011 2:38 AM

Dear all,

how to measure the earth resistance of a earth pit.( which reference)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#1

Re: earth resistance

02/14/2011 4:55 AM
  • BS 7430:1998 – 10.2

And there is another equation which you should look up yourself, as I am being busy with other stuff. Heheheheheheh...

__________________
--
Reply Score 1 for Good Answer
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#7
In reply to #1

Re: earth resistance

12/27/2011 3:48 AM

That is theoretical and it is measured by earth resistance tester called Megger practically. I would refrain from posting the test setup and test procedure :)

__________________
--
Reply
Associate

Join Date: Jan 2015
Posts: 46
#8
In reply to #7

Re: earth resistance

01/26/2016 8:05 AM

Dear,

I have been asked to calculate ground resistance test. I've searched the internet (thoroughly) but I'm still confused.

It's a fabrication shop. Bare copper cable is installed around the shop and rods are driven at 3 different locations (connected to that bare copper of course :).

Now what I'm able to understand is that I have to perform fall of potential test ONLY which I did. Below is the summary of the test:

P=voltage rod, c=current rod, E=earth electrode under test

Rod 1

E at 6 meters from P and 12 meters from C

resistance =1.9 ohm

Rod 2

E at 6 meters from P and 12 meters from C

resistance =0.8 ohm

Rod 3

E at 6 meters from P and 12 meters from C

resistance =2.2 ohm

Is this test enough? Or are there any other tests? Because only this test doesn't make sense to me as it shows resistance of electrode, contact and surrounding earth but doesn't take into account the resistance of ground grid etc.

My question is too long. I would really appreciate your response.

thanks

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: How to Measure Earth Resistance?

02/14/2011 10:13 AM

IS 3043-1987

Reply
2
Active Contributor

Join Date: Feb 2011
Location: Pakistan
Posts: 18
Good Answers: 2
#3
In reply to #2

Re: How to Measure Earth Resistance?

02/15/2011 9:13 AM

Depanding upon the application, The NEC has prescribed "Make sure that system

Impedance to ground is less than 25 ohms like Houses, buildings atc specified in NEC 250.56. In facilities with sensitive equipment like industry, Telecommunication, very high buildings etc it should be 5.0 ohms or less."

There are four types of earth ground testing methods available:

Soil Resistivity (using stakes)

Fall-of-Potential (using stakes)

Selective (using 1 clamp and stakes)

Stakeless (using 2 clamps only)

depending upon the application, where u want to measure it, the appropriate method can be used.

In market, a variety of "Digital earth Ground resistance testers" are available which make the subject very easy.

Reply Good Answer (Score 2)
Commentator

Join Date: Aug 2011
Posts: 76
#6
In reply to #3

Re: How to Measure Earth Resistance?

08/24/2011 2:07 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Reply Off Topic (Score 5)
Member

Join Date: Jun 2011
Posts: 6
#4
In reply to #2

Re: How to Measure Earth Resistance?

06/14/2011 4:48 AM

Dear sir

Please tell me what is coordination lus ix vi vi volts and vi iii iv iii i o vii vi vi amps add will leads to contact resistance.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #4

Re: How to Measure Earth Resistance?

06/14/2011 5:08 AM

Greek & Latin to me!!!!!

Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: