Compensating Cable Substitution

02/14/2011 12:42 PM

Dear all as we know we r using compensating cable for carrying mV of thermocouple . I want to know what is the resistance of that cable per unit length. Can we use copper cable in place of that, as the resistance of Co cable is less than that. Is there any other parameter coming in to place. please clarify me. JITENDRA

__________________
"MAKE CHANGES BEFORE THEY ARE FORCED UPON YOU." "PROBLEMS ARE SIMPLY CHALLENGES WAITING FOR SOLUTIONS TO MEET THEM"
Register to Reply
Pathfinder Tags: compensating cable
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: compensating cable substitution

02/14/2011 12:58 PM

Measure it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#2

Re: Compensating Cable Substitution

02/14/2011 6:15 PM

1) The resistance of thermocouple extension wire is much higher than the corresponding gauge copper wire.  Tables showing T/C wire resistances can be found using our friend, Google. 2)  It is absolutely forbidden to substitute copper cable for thermocouple extension wire.  This is an axiom of physics. 3). Many analog inputs have a limit to how much wire resistance the input can tolerate. 4). The need for long run copper cabling for thermocouple measurement was addressed some 50 years ago with the use of '2 wire loop powered temperature transmitters'.   The thermocouple connects locally to the transmitter 'out at the process' and the transmitter sends a 4-20mA current signal back to the receiver (DCS, PLC, controller, recorder, indicator) over copper wire.   The technique is suitable for very long distances.    Our friend Google will gladly amplify on this subject for you. 5). The chemical symbol for copper is Cu, not Co.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#3
In reply to #2

Re: Compensating Cable Substitution

02/14/2011 6:24 PM

The iPhone is hopelessly out of its league trying to edit posts. The gargantuan paragraph above displayed perfectly as separate, itemized sections (paragraphs), but the layout changed radically when submitted. The iPhone cannot navigate in the edit window. Technology is only great when it works.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5
In reply to #3

Re: Compensating Cable Substitution

02/16/2011 7:40 AM

I had the same problem with Opera, Bud, I have to use Firefox (Internet Exploder also works) when I make posts, else paragraphs get merged - also the toolbar for inserting images, bullets/numbers, special characters e.g. β does not appear and you cannot insert.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Compensating Cable Substitution

02/15/2011 2:44 PM
  1. A thermocouple cable is used to connect a thermocouple if you want accuracy.
  2. That means for Chromel Alumel [NiCr-NiAl] thermocouple you use NiCr and NiAl leads of the same alloy as the thermocouple.
  3. Compensating cable uses cheaper materials which around ambient temperatures have the same e.m.f. versus temperature as the thermocouple alloys. Much away from normal room temperatures you get errors.
  4. If you use copper cable you will get a temperature error equal to the difference of temperature between the terminals at which you connect to the thermocouple leads and that of the terminals on the measuring instrument. This error is usually too much to accept, especially since it is variable and difficult to know.

Look at website www.tc.co.uk and get the free guide. Read it, learn it and think about it.

Website www.omega.co.uk also has useful free manuals, some down-loadable.

Register to Reply Score 1 for Good Answer