Rerlay amps setting for Star delta motor

02/15/2011 6:23 AM

30Kw Motor rated amps is51 on name plate of motor,controlled by star delta starter,wht to be relay amps to be kept

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#1

Re: Rerlay amps setting for Star delta motor

02/15/2011 6:27 AM

ask the manufacturer regarding the allowable limits and consult with a experienced commissioning engineer. dont go just like that bcoz it may damage the motor if proper settings are not adopted. Or refer the relay manual , you may find some information.

__________________
You don't understand anything until you learn it more than one way.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Rerlay amps setting for Star delta motor

02/15/2011 6:37 AM

Set the overload to the same setting as the full load current on the motor plate.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Rerlay amps setting for Star delta motor

02/15/2011 7:06 AM

If the relay is in the main circuit, you need to set it to 51A. If it is within the delta (see diagram), you need to set it to 51÷√3 = 30A

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Rerlay amps setting for Star delta motor

02/15/2011 7:37 AM

Here we go again!

Where to put the overloads

see http://cr4.globalspec.com/thread/63668

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Rerlay amps setting for Star delta motor

02/15/2011 9:20 AM

As TonyS and kvsridhar have pointed out, there are several ways to configure the motor Over Load Relay when using a Star (Wye) Delta motor starter. Their illustrations show 3 different valid connection diagrams. Depending on how yours is set up, the selection of the OLR settings will either be 100% of the motor FLC or 58% of the motor FLA. Only you can determine which one you have, and to do so you will need to observe and understand the OLR location in your connection pattern. If this is beyond your capabilities, please consult a professional in your area who can understand it. The ramifications of getting it wrong could be disastrous.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#6

Re: Rerlay amps setting for Star delta motor

02/15/2011 12:16 PM

u have not mentioned the application of motor

i suggest to set the relay setting greater than 4 or 5 amps of it normal running ampers

i.e., if normal running ampers is 35A it is beter to set relay at 40A

__________________
key questions why, what & how - just think
Reply Score 2 for Off Topic
Anonymous Poster
#7
In reply to #6

Re: Rerlay amps setting for Star delta motor

02/15/2011 7:53 PM

Relay must be set to actual current, not higher ! Please do not give wrong advice, it can be dangerous.

Reply
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#10
In reply to #7

Re: Rerlay amps setting for Star delta motor

02/27/2011 10:50 AM

i have explained it taking the condation that the motor is drawing current less than the rated current while running on load. if it is running by drawing full load current in normal load condation it is good to set relay setting to rated current setting of motor

__________________
key questions why, what & how - just think
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #10

Re: Rerlay amps setting for Star delta motor

02/27/2011 11:10 AM

The main thing is ... a 10HP motor can indefinitely take the appropriate current, say 16A. Any overcurrent beyond 16A is detrimental to the motor, but any current upto and including 16A is not. So, even if the load is 7.5HP, you can set it to to 10HP (16A). NOT higher than this.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Rerlay amps setting for Star delta motor

02/16/2011 8:35 AM

Having had to tackle a motor fire after some fool upped the O/L's I will always set the relay to the motor rated current.

If you need to raise the O/L settings the motor isn't big enough!

It's only common sense!

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #8

Re: Rerlay amps setting for Star delta motor

02/16/2011 12:49 PM

TonyS,

Methinks, after parsing the statemenst in post 6 & 7 (and applying my experiences in this forum) that they are under this very common mistaken belief that motor OL protection should be set for the LOAD current, not the motor FLC from the nameplate, which hopefully also meant "as long as the load current is blow the FLC rating of the motor".

You and I know differently, but I have discovered that this is an all too common practice. I guess people think it provides closer protection? I don't really know why they do it though. Personally I would never do that because it just sets the system up for nuisance tripping, and repeated nuisances like that cause people (fools) to do things like set them TOO high and smoke the motors, as you experienced.

It keeps motor rewind shops in business though, maybe they are the ones surreptitiously planting that information!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Reply to Forum Thread 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (2); kvsridhar (2); parvathaneni (2); PWSlack (1); TonyS (2); vijaymail_electrical (1)

Previous in Forum: Transformer Vector Group   Next in Forum: UPS Load

Advertisement