Star / Delta O/L’s - Which is Correct

12/15/2010 4:57 AM

I've always worked on plants that had substantial power available so star delta starters were rare to come across. So not having a lot experience with them I've always been confused as to which is the correct method of connecting the overloads A or B. both work, but one must be the "correct" way. I prefer method A as the O/L settings are easy to understand.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Star / Delta O/L’s which is correct

12/15/2010 5:09 AM

A is correct. The overload should always disconnect all power from the motor. B cannot do this.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: Star / Delta O/L’s which is correct

12/15/2010 5:23 AM

Sorry PWS I didn't make it clear that the O/L relay would be in the control so as to drop the line contactor out. Not breaking the circuit it's self.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#3

Re: Star / Delta O/L’s which is correct

12/15/2010 5:27 AM

Yes but - as in the other thread - it's use is more about accelerating a large load i.e. big machines.

So which acceleration phase takes more 'stall current seconds' is the one with 'extra protection.

Both are over and above protection (not shown) ahead of the primary switch.

Or both are correct - depending.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#20
In reply to #3

Re: Star / Delta O/L’s which is correct

12/17/2010 8:05 AM

Now you're absolutely certain that you're not being indecisive about this?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#21
In reply to #20

Re: Star / Delta O/L’s which is correct

12/17/2010 4:38 PM

Heeeeheee - 17 posts on and has "it depends" changed?

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#24
In reply to #21

Re: Star / Delta O/L’s which is correct

12/18/2010 8:47 AM

Nothing really changed other than my mind, following some of the reasons put forward I'd now opt for "B" if forced in to it.

I still don't like either of them!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#25
In reply to #24

Re: Star / Delta O/L’s which is correct

12/18/2010 7:08 PM

And I don't like the idea of 4 x 866A's as a bridge, but it's handy to understand the principals - well I think so - because you never know when it might come in handy somewhere totally different.

(follow this link in that post)

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: Star / Delta O/L’s - Which is Correct

12/15/2010 7:44 AM

Both are correct. In A the O/L has to be set at the line current, while in B it is to be set at phase current. In B, it is a smaller relay, and, sometimes, cheaper (direct vs CT-relay). Most Indian and European starters are wired like B.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #4

Re: Star / Delta O/L’s - Which is Correct

12/15/2010 10:29 AM

+1 GA.

As he said, both work, both are "correct" but the reason you don't see "A" everywhere is strictly economic. If it is a 50HP motor, it probably makes no difference, the cost of a 50HP rated OLR is probably almost the same as that of a 30HP OLR (58% of the size). But if it is a 100HP motor, the OLR in "A" would have to be a more expensive version that can carry line current. Then if it's a 500HP motor, it's back to being a toss-up because either way, you have to use CTs for the OL, and what's the difference in the cost of 1000:5 CTs vs the cost of 600:5 CTs? Next to nothing.

Personally, I like to use "A" because I tend to hate Star-Delta anyway and if someone insists, doing it with method "A" leaves open the possibility of using any other starting method in the future once the user figures out that Star-Delta is costing him money in torque damage. but that's just me...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Star / Delta O/L’s - Which is Correct

12/15/2010 11:05 AM

Count me in too. After your very valid and eloquent recommendation of drives as against ΥΔ in another thread, i am spreading that gospel among my clients and their customers with some vim and vigour. i hope good sense prevails over money sometimes

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#5

Re: Star / Delta O/L’s - Which is Correct

12/15/2010 7:46 AM

A and B has same function. In both case the main Contactor only open. Doesnt matter whether o/L is located. It is important which contactor is connected through.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#8

Re: Star / Delta O/L’s - Which is Correct

12/15/2010 1:09 PM

B is correct. In this connection O/L relay is set at phase value of current of the motor giving protection to motor in star as well as delta connection. The relay would get true thermal image of motor.

__________________
When was last time you did something for first time.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#12
In reply to #8

Re: Star / Delta O/L’s - Which is Correct

12/16/2010 12:48 AM

Dear Happy Singh

Your reasoning is good and most acceptable.

R.Panneer Selvam

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#16
In reply to #12

Re: Star / Delta O/L’s - Which is Correct

12/16/2010 6:56 AM

thanks

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14
In reply to #8

Re: Star / Delta O/L’s - Which is Correct

12/16/2010 4:19 AM

GA from me.

This is the real answer for the B design. Better protection for star running in case it got stuck in that stage.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: Star / Delta O/L’s - Which is Correct

12/15/2010 4:50 PM

I don't suppose there is or ever will be a right answer. I dislike star delta but if forced I'd go for A.
As I said in my OP I'm used to plants where you could start 400HP motors DOL without trouble. The only time I came in to contact with YΔ is with items of kit bought with the electrics as part of the package.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#10
In reply to #9

Re: Star / Delta O/L’s - Which is Correct

12/15/2010 5:41 PM

Perhaps the 'right answer' is it's about the only way you could do it, before 'modern electronics'.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Commentator

Join Date: Aug 2010
Location: alabama
Posts: 81
#11

Re: Star / Delta O/L’s - Which is Correct

12/15/2010 9:35 PM

as being lucky to work in mills where we use what we got. 'b' would be the most familar one for myself, we would use that set-up w/ ct's for high inrush currents; i.e. chippers, hogs and other cutting loads - and 'a' w/ motors of low inrush currents; i.e. conveyors or transportation belts.

__________________
MattJohnson
Register to Reply
Anonymous Poster
#13

Re: Star / Delta O/L’s - Which is Correct

12/16/2010 1:26 AM

METHOD B IS THE CORRECT PROCEDURE.

THIS ALSO REMOVES ALL the POWER AS WITH THE OPERATION OF THE OVERLOAD THE MAIN CONTACTOR DROPS OUT.

THE RATING OF THE O/L RELAY SHOULD BE 0.58Ir ,and is universally adopted by SIEMENS/SCHNEIDER/ABB etc .

Register to Reply
Anonymous Poster
#15

Re: Star / Delta O/L’s - Which is Correct

12/16/2010 4:33 AM

B is always preferred and use in practice. As Mr. Happy Singh already mentioned it is very improtant to note that the motor will get true thermal image for effective protection against overload( resulted in overheating of windings).

Register to Reply
Anonymous Poster
#17

Re: Star / Delta O/L’s - Which is Correct

12/16/2010 8:20 AM

Both are correct but when you are using star/delta starter to run the motor against the load ,for example high starting torque required and stalling current for a longer time like ID Blowers i prefer to use B,OTHERWISE due to overlaod main contactor will dropout.universally major players like L&t/SIEMENS/SCHNEIDER/GE PREFERS METHOD -B and economical. Method -A is preferable for lighter /smoother loads.i hate star delta starters for large machines better to use,soft starters.

Register to Reply
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#18
In reply to #17

Re: Star / Delta O/L’s - Which is Correct

12/16/2010 9:23 PM

Let me explain it with an example of 50 KW, 380V motor. The motor current is 50,000 / (1.732 x 380 x 0.8) = 95A (approx). The motor has star delta starting option. So, the motor is designed to operate at 380V continuously with its winding delta connected. The rated line current for the motor is 95A, the rated current of the winding is 95 / 1.732 = 55A (approx.). During the star operation (short time) of the motor, the line current is equal to winding current and so the motor should be protected for maximum line current 55A for star.

Now consider the case A:

Here the O/L protection is installed in the line. The setting of the relay is set for 95A protection. This setting is perfectly works for the delta operation but it is much higher for star operation. Because the line current is 55A (for star), but setting is 95A. Since the motor runs very short time in star operation, we can ignore the overload protection for this short time period. But what happens when the star-delta timer mal-functions (keeps motor to operate in star for longer period) and the motor is overloaded in this period? The motor will be damaged.

Case B:

In this case, the O/L is installed in series of winding and its setting is set for 55A protection. The overload protection of the motor is always protects the motor. The rating of O/L is also required less (58%) and may also save money, as already indicated by JRaef.

Conclusion: Both are correct but the case B is more safe and preferable. With case A, there is a sort of risk, though the probability is very low (simultaneous occurance of the timer mal-function and motor overload during starting)

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#19
In reply to #18

Re: Star / Delta O/L’s - Which is Correct

12/17/2010 5:23 AM

Cheers, msamad, as I said there're not something I've had a lot to do with and I don't like them. Following the episode with the 800HP starter in an earlier thread http://cr4.globalspec.com/thread/60397 I've gone right off them!

The only reason I asked the question was out of curiosity. The reason for my preference for method A was simply ease of understanding the O/L setting, but you've made me change my mind. Not that I intend to install any of the horrible things unless I'm forced. Now I'm retired I can't be forced anyway

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster
#22
In reply to #19

Re: Star / Delta O/L’s - Which is Correct

12/18/2010 2:07 AM

BOTH ARE WRONG sorry guys i have to shout here. In delta connection there is a necessity to connect motor rotar wingings in proper phase sequence.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#23
In reply to #22

Re: Star / Delta O/L’s - Which is Correct

12/18/2010 2:22 AM

Oh - here we go again

Why don't you go and back door a thread - learn what you need to know, then never come back and say "oh now I get it" to the person you are yelling is "wrong!"

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#26
In reply to #18

Re: Star / Delta O/L’s - Which is Correct

12/19/2010 2:33 PM

Not that this thread needs to drone on further with more indeterminate outcomes, but I have to differ on a point in msamad's post.

"Now consider the case A:

Here the O/L protection is installed in the line. The setting of the relay is set for 95A protection. This setting is perfectly works for the delta operation but it is much higher for star operation. Because the line current is 55A (for star), but setting is 95A. Since the motor runs very short time in star operation, we can ignore the overload protection for this short time period. But what happens when the star-delta timer mal-functions (keeps motor to operate in star for longer period) and the motor is overloaded in this period? The motor will be damaged.'"

Where is the damage going to come from? The motor winding current is rated for 95A. If the line current is 55A and the timer malfunctions, leaving it in Star indefinately, we can assume that the motor torque will be insufficient to fully accelerate the load and it goes into a stall condition. In that condition, the motor winding current would theoretically rise to Locked Rotor (once the rotor stopped moving, which actually would not happen, but let's look at worst case scenario). LRC would be 600% of FLC, but because it is stuck in Star, the maximum developed current will be 33% of that, so 200% FLC. The OL trip curve will of course take longer to trip at 200% FLC, but that STILL is the same thermal damage curve of the motor windings, it STILL should be adequately protecting that motor. i.e. any damage is no different than if the OL were in the B location. It's all relative.

So once again, no different.

And by the way, anyone who uses Star-Delta without an incomplete sequence trip should have their head examined. But of course, that adds COST, which is the ONLY reason anyone uses Star-Delta in the first place, so it never happens...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#27
In reply to #26

Re: Star / Delta O/L’s - Which is Correct

12/19/2010 4:47 PM

Thanks JRaef for your comment. The more we discuss, the more we get benefited from this forum. What I am indicating here is not the disagreement; it is just what I think how it is. Again come back to the case that I described.

(1) The motor winding rated current here is 55A (not 95A, since motor FLA is 95A and the winding is designed for Delta connection; the winding current is 58% of motor rated current. For Delta circuit, the line current is 1.732 times the phase current).

(2) The O/L relay for case A must has to be set for 95A (based on motor FLA).

(3) If motor runs Y continuously, I agree the motor torque and hence power is reduced to 33%, so motor's power is reduced to 16.67 KW (50/3). But the 220V (380/1.732) is being applied across the motor winding. So, the motor current is 16,670 / (1.732 x 220 x 0.8) = 55A. If the motor is 50% overloaded, the motor will draw 82.5A. The relay setting is 95A for case A and the motor will never trip with the 50% overload in Y run and if the condition prolonged, the motor may damage (because the motor winding is rated for 55A).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (5); Anonymous Poster (5); Happy singh (2); JRaef (2); kvsridhar (2); LAA_Lucke (1); MattJohnson (1); msamad (2); Panneer Selvam (1); PWSlack (1); TonyS (5)