Fault on a Star/Delta Starter

09/25/2010 12:41 AM

A mate has asked me if I'd help him with a fault on a star/delta starter. It's a beast of a thing 800HP closed transition change over. The starter even has it's own 800KVA 11/.44KV transformer.

He's sent a drawing but it's that old it's like trying to piece the dead sea scrolls back together. Could someone just confirm the sequence of these things for me, it's been a long time since I had anything to do with them.

A/ main contactor closes

B/ star contactor closes

(time delay)

C/ transition contactor closes

(small time delay)

D/ star contactor opens

(small time delay)

E/ delta contactor closes

(small time delay)

F/ transition contactor opens

Apparently every so often the O/L's trip on start up opening the 11KV OCB (the O/L's, P&B Goulds are wired to the OCB direct and not the contactors) at the transition point. All my mate says is there's one hell of a flash and bang when it trips. I don't think he's to keen to look that closely when it does!

Any ideas would be welcome as well.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Fault on a star/delta starter

09/25/2010 2:08 AM

In my experience, this kind of flashover happens when the arc chute of an opening contactor has some ionised air still when the other contactor closes, causing a flashover. i have seen it quite often in open transition ΥΔ starters without the 50ms transition delay between star contactor open and delta contactor close situation. Can't say whether a similar situation can happen in closed transition ΥΔ....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Fault on a Star/Delta Starter

09/25/2010 10:00 AM

Here is a link to the website of a friend of mine which shows a diagram and sequence for closed transition S-D starting.

Just out of curiosity, how would he see an arc flash with an Oil Circuit Breaker? Or did you mean ACB, Air Circuit Breaker? That would make a lot more sense. If so, I have never seen an ACB operate under load without creating a flash, that's why I never use them. And I would change that OL protection scheme to operate the contactor control circuit, not the up strea breaker. Contactors are designed for multiple operations, circuit breakers are not really, they technically should be recalibrated after multiple trips like that and they may need to be rebuilt now.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: Fault on a Star/Delta Starter

09/25/2010 10:25 AM

The O/L's (P&B Goulds) trip the OCB rather than the main contactor. In normal operation the contactors stop the drive. We found the fault to be the star contactor being slow to open, it was only partially open as the delta closed. Hence the almighty flash and bang. I'd got the panel door open when it failed, I nearly had to go and change my underpants!

The fault was a worn pivot bearing, and a bad connection on one of the opening coils capacitor.

The contactors are old BHI things left over from the building of the ark. The contactors have 3 coils, 1 per phase to pull them in and opening coils fed by capacitors. It's DC control just to add to the fun.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #2

Re: Fault on a Star/Delta Starter

09/25/2010 10:43 AM

Thanks for the site, it was already in my favourites list but I didn't think to look at it before this little adventure.

PS the OCB's are well maintained. Not that they're anything to do with me, I just got involved in this as a favour.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #2

Re: Fault on a Star/Delta Starter

09/25/2010 12:46 PM

GA to you JRaef, better put than what i could. i did say ionised air...well.... c'est la vie.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Fault on a Star/Delta Starter

09/25/2010 6:59 PM

It probably was ionised air in the star contactor that caused the flashover. The air gap wasn't wide enough due to the slow operation of the contactor at the moment full voltage was applied by the delta contactor.

If you've worked on BHI gear you'd know it will stand up to anything you throw at it, totally over engineered. Considering this gear is near 50 years old it just took things in it's stride.

As for breakers not withstanding repeated operation, how can we use whatever type of breaker for repeated starting of large drives?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Fault on a Star/Delta Starter

09/25/2010 9:22 PM

For sure it was ionizing in the contactor. If there were vents in the doors you can see the blue flash when it happens. Not that uncommon with air contactors. I once replaced one with vacuum contactors, the user had a hard time believing it was working because he didn't see a blue arc flash.

And you sir have major kahunas for being willing to operate a MV star-delta starter built with air contactors when the door is open! I've done it on a 5kV solid state soft starter, there was an eerie creeping blue plasma phenomenon crawling all over the conductor insulation like a living spider web. Freaked me out...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Fault on a Star/Delta Starter

09/26/2010 2:59 AM

It was a bit daunting to operate the gear with the doors open, especially as we were expecting a bang. I will admit I didn't stand to close. And as I said I was very close to having to change my underpants when it did go bang! But we soon found the problem area!

I've a lot of faith in BHI gear, I once came across a crane long travel control panel that someone had maintained (supposedly), they had left every arc chute on the floor! The LT drive motors were 2 X 60HP wound rotor both wired to one set of contactors, normal braking operation would be to reverse the motors while still travelling. The panel was working quite happily, although it did look like a firework party.

You would have loved these crane panels. Each of the crane main booms were switch rooms each had open contactor panels over 60' long. The only thing to stop you falling on to the panels was a single handrail.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".