Anonymous Poster

Lighting Transformer

02/21/2011 10:31 PM

Why 100 kVA lighting transformer is used in the power substation, while the voltage ratio is 415/415V,delta-star winding scheme ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Lighting Transformer

02/21/2011 10:37 PM

Maybe the lighting circuits are phase-to-neutral 240V, not available on the primary side?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Lighting Transformer

02/21/2011 10:57 PM

Because that's what the Engineer designed it to be. If you look at the Engineering prints you'll find his name there. Send him an inter office e-mail and ask him.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Participant

Join Date: Dec 2010
Posts: 3
#3

Re: Lighting Transformer

02/22/2011 1:39 AM

Generally in a power station the 415 V supply is three wire.There is no neutral. Lighting is generally connected between phase and neutral. Hence, as a neutral has to be created a lighting transformer is used.

Regards,

S. V. Iyer

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Lighting Transformer

02/22/2011 7:52 AM

Dear Guest,

In the Sub-Station -in the Step-down Transformer there may not be NEUTRAL. For Single Phase Circuit, NEUTRAL IS REQUIRED hence a small Transformer is used.

DHAYANANDHAN.S., INDIA

Reply
Anonymous Poster
#5
In reply to #4

Re: Lighting Transformer

02/22/2011 9:16 AM

There's an echo around here

Reply
Active Contributor

Join Date: Jan 2011
Posts: 15
Good Answers: 1
#6
In reply to #4

Re: Lighting Transformer

02/22/2011 11:12 PM

You are absolutely right. Another reason is to limit the fault level.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7

Re: Lighting Transformer

02/22/2011 11:50 PM

What is the rated voltage of generator?. If not 415V,a step down transformer with secondary voltage of 415V and earthed neutral could be used.

__________________
pnaban
Reply
Anonymous Poster
#8

Re: Lighting Transformer

02/23/2011 2:38 AM

Lighting transformers are usually installed to ensure the lighting supply voltage remains at the optimum level necessary for increased life of the fittings and lamps, over voltage can reduce this considerably.

Reply Score 1 for Off Topic
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#9

Re: Lighting Transformer

02/23/2011 7:06 AM

Delta/ Star (neutral grounded) is used in substation for for the following reasons:

For electrical isolation in case of occurence of fault from primary side of transformer( i.e main L.T. Bus feeding from main transformer)

High % impedance of lighting transformer to restrict fault current.

__________________
Manindra
Reply
Associate

Join Date: Feb 2011
Location: Angul, orissa
Posts: 25
Good Answers: 1
#10

Re: Lighting Transformer

02/24/2011 5:35 AM

Generally lighting loads suffer from frequent short circuits. Hence to isolate the main system from these disturbances, a lighting transformer with a delta star scheme may be used.

__________________
mscs
Reply
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#11

Re: Lighting Transformer

03/19/2011 5:00 AM

Dear All, In our plant we use a 415/433 V lighting trafo for lighting distribution through LDB. Usually it is provided with Off Circuit Tap Changer to adjust the voltage on the Load Side when ever the Incoming Voltage increase or decreases. Through the star side single power for single phase load can be derived.

__________________
"Engineering is Passion"
Reply