Anonymous Poster

Loading of Transmission line

02/25/2011 1:01 AM

Is loading of 400 kV transmission line of 12 km with just 20 MW too light??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Loading of Transmission line

02/25/2011 2:31 AM

With that much information it is difficult to say.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Loading of Transmission line

02/25/2011 8:02 AM

Since a 400 kV line is usually built to carry about 500 MW, 20 MW is not very much!

The capacitance of 12 km of line would draw about 10 amps charging current (7 MVA). 12 km is too short to see any transmission line effects [like receiving end volts higher than source end!] N.B. wavelength at 50 Hz is about 1500 km. But I wonder about power factor effects of transformer magnetising current on a generator or resonance at even smaller loads - if this is not yet Grid connected.

How much lagging transformer magnetizing current do you see before connecting to this line? What is Transfo rating and ratio from generator?

Reply
Anonymous Poster
#3

Re: Loading of Transmission line

02/28/2011 4:35 AM

calculate the surge impedance loading and then compare. u can calculate it using

surge impedance loading = (V*V)/Zc; where Zc = sqrt(L/C); where L is the inductance of the transmission line and C is the capacitance.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4
In reply to #3

Re: Loading of Transmission line

02/28/2011 8:03 AM

For a British 400 kV line with 2 x 258 mm² conductors, the surge impedance is 296 ohm and the corresponding matched load 540 MW [(400/√3)²/296] . Hence my "about 500 MW". Since we do not know how many conductors/phase, size or spacing or inductance/capacitance values one cannot be more accurate. But the actual question was "is 20 MW too small a loading". A 500 MW line is not stressed by 20 MW, so it is a question of effect on connected items and we do not know anything about them.

Reply