Value Engineering Power Transmission

02/25/2011 10:13 AM

I'm very experienced at designing and installing PV systems from 1 to 30KW DC, usually using multiple inverters in a grid tie setting, producing 208,240 or 277 VAC. I consistently find [very smart] people eager to take both sides of the following question.

At a distance of 500 feet from the 450VDC production point array to the AC meter/panel grid tie point, where is the ideal place to perform the inversion, and why.

I'll start the ball rolling with a voltage loss versus power delivery efficiency, and a price of conductor comparison. Trenching is a given.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: Value Engineering Power Transmission

02/25/2011 2:07 PM

I would put the inverters close to the main power panel and run the DC to it with a two wire lead.

Reason being their is not a long run of three or four line wire needed to connect the inverters to the main service plus less potential for line noise or transient AC related problems and false over voltage tripping due to the long run of line resistance on the AC side in theory. With the long run of DC that potential noise can easily be filtered out with a simple capacitor bank and surge suppressor plus the voltage rise from line losses is far less likely to cause any real problems.

Thats my theory's and reasonings anyway.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Value Engineering Power Transmission

02/25/2011 8:11 PM

Your combination of voltages is interesting. The lower AC voltage would require higher amps, but the 3-phase rather than 1-phase would be less by about the same √3 factor; and then 3 conductors rather than 2 (ignoring neutral for the moment). With tcmtech, I (think I) favor the inverter closer to the AC end, but would wonder about dogmatism one way or the other.

It might be amusing to see the various reasonings on either side of this.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 61
#4
In reply to #2

Re: Value Engineering Power Transmission

02/26/2011 4:53 AM

I designed systems to run from a 3-phase AC feed, with the rectifier close to the inverters. The main reason, was that one of the inverters supplied multiple motors whose speed was being modulated. The regen into the DC bus could be used to reduce power from the AC supply to the other inverters and avoid using large braking resistors.

Have also used a rectifier with DC distribution to the inverters. Used a large capacitor bank close to the inverters to provide dip-proofing for about 300 milliseconds on AC supply loss.

Depends on application, one way or the other.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 344
Good Answers: 17
#3

Re: Value Engineering Power Transmission

02/26/2011 2:54 AM

If single phase AC:

On the basis of current and therefore cable size and cost, go short DC and long AC (for all AC voltages specified).

On the basis of potential corrosion both in cable and in nearby pipes, go short DC and long AC.

No argument.

If 3 phase AC, this is again an economics problem. You need to cost the cable involved, both DC and AC, and do the sums.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 344
Good Answers: 17
#5
In reply to #3

Re: Value Engineering Power Transmission

02/26/2011 5:05 AM

Oops! for single phase AC with 450V DC lower current than AC line so long DC and short AC.

Economics will probably decide the solution.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jan 2011
Posts: 61
#6
In reply to #5

Re: Value Engineering Power Transmission

02/26/2011 5:17 AM

True. Economics dictate which to use.

Register to Reply
Commentator

Join Date: Jan 2011
Posts: 61
#7
In reply to #6

Re: Value Engineering Power Transmission

02/26/2011 5:34 AM

DC links.

Avoid using DC over many miles with earth return. Gosh, the environmental damage is incredible. If you've ever flown over the DC link from Mozambique to South Africa, and seen the corrosion in the rock formations, you'll understand.

We are discussing short distance distribution here.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Dave Simpson (3); Phaddy (2); tcmtech (1); Tornado (1)

Previous in Forum: Spent Nuclear Rods for Power Production   Next in Forum: A Potential Solar Energy Over Supply In Germany

Advertisement