I have a INCOMIING 100A mccb TPN c/w ELR 25ka and have a lenght of 80M from MSB to DB cable sizing 70mm main subboard fault level setting at 45ka, i need a ka selection formula to justfy 25ka the design MCB AND RCCB both 63A DP per circuit with L1 43A, L2 32A, L3 44.3A. Appreciate if some one could provide me the formula for Ka and cable sizing.
Regards
Jeff
Re: KA selection
02/25/2011 9:40 PM
Speaky Engrish!
Re: KA selection
02/26/2011 12:16 AM
Yes, thank you for your time to look into this.
Re: KA selection
02/25/2011 11:12 PM
ka = (L1^2 + L2^2 + L3^2)^-3*(L1+L2+L3)/(L1*L2*L3)
Re: KA selection
02/26/2011 12:11 AM
Can you prove it?.
pnaban
Good Answers: 19
Re: KA selection
02/26/2011 12:57 AM
step1 Prepare Single line diagram
step 2 Enter cable size,length.
step 3 Get input fault level from utility provider.
step 4 Get the cable resistance and reactance
step 5 calculate the fault level at various points MSB,DB and load end.
step 6 Based on step 5,calculate the fault current at various points.
step7 Now check the interrupting rating of MCCB,MCB etc these rating should be greater than the fault current.
Ramesh,Freelance Electrical/automation Consultant
Re: KA selection
02/26/2011 10:44 AM
Ravinod, have you had you humour glands removed?
Re: KA Selection
02/26/2011 2:35 PM
I am providing you with the method rather than a formula so you will never have to ask again. go here. The cable size required is larger enough to carry the load per your local code.
Similar answer as ramvinod