ABS Rules

03/01/2011 3:20 AM

Medium Voltage distance between phase to phase to ground for an 11kV switchgear as per ABS rules is 120mm, but the SWBoard Manufacturer only provide 75mm and insisted that it is ok in one of our Drilling Rigs. I am the E&I Inspector and dis-agreed but the bosses accepted! This is really bad!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: ABS Rules

03/01/2011 3:34 AM

Determine if the gap is only air, or if there is also some other insulating barrier. (Which you might even be able to add after the fact.)

Otherwise, send the bosses a signed memo that if the installation blows up, it will blow up in their faces!

I can't tell which risk is greater: the electrical risk or the political risk. Whatever else, don't stick your hand into the gap!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Associate

Join Date: Oct 2009
Posts: 47
#2
In reply to #1

Re: ABS Rules

03/01/2011 5:08 AM

YES CORRECT

Reply
Associate
Netherlands - Member - New Member Canada - Member - New Member

Join Date: Oct 2010
Location: Canada
Posts: 41
Good Answers: 2
#4
In reply to #1

Re: ABS Rules

03/01/2011 7:39 AM

My sentiments exactly.

__________________
I do not feel obliged to believe that the same God who has endowed us with sense, reason, and intellect has intended us to forgo their use. Galileo Galilei
Reply
Commentator
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jan 2011
Location: India
Posts: 69
#3

Re: ABS Rules

03/01/2011 5:37 AM

Mr. Tornado is right.... and inform higher authority about mode of risks.......

Reply Off Topic (Score 5)
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

amith (1); jk (1); sridharganasen (1); Tornado (1)

Previous in Forum: Instruments needed forIlluminance Testing Lab   Next in Forum: d.c.motor
You might be interested in: Drilling Rigs, Rules and Scales, Mining Machines

Advertisement