Need Advice on Cable for Service Voltage 20 kV

03/03/2011 10:45 PM

Dear All,

if my service voltage 20 kV, can i use 12/20 kV N2XSY cable or must 18/30 kV ?

regarding to IEC standard and concidering voltage discharge.

thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: need advice cable for service voltage 20 kV

03/04/2011 12:33 AM

I'm getting more and more worried about the quality and integrity of electricians around the world. There should be somebody on site properly educated and authorized to read and decide from the IEC standard which type of cable you should use. If I said yes to either of these cables and they immediately burst into flames and took out your entire installation, will you blame me for the damages? If I said that neither are suitable for the installation, would you buy a more expensive cable on my word.

If you don't have this standard yourself and are looking for me to tell you what it says, I say buy the standard yourself.

I'm not even sure if the IEC standard is the appropriate standard for your location.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: need advice cable for service voltage 20 kV

03/04/2011 7:03 AM

Is your system earthed or unearthed? if earthed, is it solid earthing or impedance earthing?

Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#7
In reply to #2

Re: need advice cable for service voltage 20 kV

03/07/2011 10:44 PM

Dear electricalexpert65,

my system is Solid Grounding at low voltage side (transformer 11/20 kV)

thank you

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #7

Re: need advice cable for service voltage 20 kV

03/08/2011 8:14 AM

If your LV Side (11kV) is solidly earthed, I assume that your 20kV side is unearthed. Ans that is the side for which you want to select a cable. If so, you have to select a 20kV (UE) Grade Cable.

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#3

Re: Need Advice on Cable for Service Voltage 20 kV

03/04/2011 11:12 AM

Somewhat Vague Question:

"if my service voltage 20 kV, can i use 12/20 kV N2XSY cable or must 18/30 kV ?"

Somewhat Vague Answer:

http://www.ddacables.com/katalog/pdf/n2xsy6-10kv_12-20kv_18-30kv.pdf

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: Need Advice on Cable for Service Voltage 20 kV

03/04/2011 8:04 PM

The cable voltage designation defined in IEC 60502, article 4.1 as:

**********

The rated voltages U0/U(Um) of the cables considered in this standard are as follows:

U0/U(Um) = 3.6/6 (7.2) - 6/10 (12) - 8.7/15 (17.5) - 12/20 (24) - 18/30 (36) kV.

In the voltage designation of cables U0/U(Um):

U0 is the rated power frequency voltage between conductor and earth or metallic screen for which the cable is designed;

U is the rated power frequency voltage between conductors for which the cable is designed

Um is the maximum value of the "highest system voltage'' for which the equipment may be used

**********

There is also three power system categories (A, B, C) defined in this article. If the system category is A or B (primarily the system disconnects for earth fault condition), you can use 12/20 (24) KV cable for the 20 KV system voltage. There are other factors also needs to be considered. I would suggest you to consult the cable manufacturer and the related standards before using the 12/20 (24) KV cable for the 20 KV system.

http://www.caledonian-cables.co.uk/DdFls/Three%20Core%20Cables%20To%20IEC%2060502.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 3)
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#5
In reply to #4

Re: Need Advice on Cable for Service Voltage 20 kV

03/06/2011 3:56 AM

It is also wise to look into other parameters and not just voltage ratings as usable life depends on many other parameters also. These specs can be found in standard cable type if specified.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#6
In reply to #4

Re: Need Advice on Cable for Service Voltage 20 kV

03/07/2011 2:15 AM

yes, msamad

i also agree with you, but there is some time, my customer complain me with saying, cable 12/20(24) has voltage discharge 20.76 kV. so what about if i tap my transformer become 21 kV (5 %), will it reduce the age of cable faster ?

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard