Can I use #6 stranded (as opposed to #6 solid) for a lightning drain off my Hamm antenna? I have the stranded but a friend thought it had to be solid. (southern Oregon). Thanks, sb

Register to Reply
Pathfinder Tags: lighting ground
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: blueskysb

03/05/2011 10:11 AM

#6 stranded is fine. It's ham, not Hamm. (Hamms is a beer)And the antenna doesn't care where it is.

I suggest you contact the American Radio Relay League.

American Radio Relay League | Ham Radio Association and Resources

Register to Reply Score 1 for Good Answer
Member

Join Date: May 2010
Posts: 5
#3
In reply to #1

Re: blueskysb

03/05/2011 11:01 AM

Thanks Lyn, I like Hamms, and with the wonderful "local code" world.....:)

Register to Reply
Power-User

Join Date: Nov 2009
Location: In the Ozark woods in missouri.
Posts: 106
Good Answers: 3
#5
In reply to #1

Re: blueskysb

03/05/2011 11:24 PM

Its just my personal preference, but solid is always electrically better than stranded.Its not the length, or thickness of the wire, but the connection points. When tightened down, the stranded can push apart, leaving less wire connected at this critical point.Less wire in contact, less protection.Some might say this is knit-picking, but I have had this happen to me. I live way out in the woods, ran out of connectors, and did not want to drop everything and drive 30 miles one way for them.So I made it a tempoary connection. Well tempoary turned into permanent, cause of too many honey do jobs, and when I really needed it, it failed.Had this been solid wire, no problem.If your going to do it, do it right the first time.If I had not run out of connectors, probably no problem.Its the wee little things that get you. Pay attention to detail, and always double check your work. 73`s KC0VEA

__________________
Life is tough, but it`s tougher if your stupid, John Wayne.
Register to Reply
Guru

Join Date: Dec 2008
Location: nj,usa
Posts: 1252
Good Answers: 33
#2

Re: blueskysb

03/05/2011 10:19 AM

#6 stranded should be fine. Most Ham systems actually call for #8.

Good luck.

Will we be hearing from you on field day in June?

__________________
CARPE CRUSTULORUM!
Register to Reply
Member

Join Date: May 2010
Posts: 5
#4
In reply to #2

Re: blueskysb

03/05/2011 11:15 AM

Over kill??? got it, use it. we'll see. Thanks not so:)

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6

Re: Blueskysb

03/06/2011 11:36 AM

Solid is better if you consider that lightning current are high frequency because of their sharp peak.

Stranded will do but will also have a relatively higher resistance to the lightning current going to earth. This might not be very significant and depends on the length of the wire etc...

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#7
In reply to #6

Re: Blueskysb

03/07/2011 1:52 PM

As you say, Lightning current is effectively high frequency, and the skin effect makes high frequencies travel mostly on the surface. Stranded wire has a lot more surface than solid of the same size, so it seems to me that stranded would actually be preferred. Am I mistaken?

Another point would be to avoid sharp corners/bends in routing the wire.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Member

Join Date: May 2010
Posts: 5
#8
In reply to #7

Re: Blueskysb

03/07/2011 5:31 PM

DK, I have heard the same thing about stranded having more conductive surface area, I know of one company that specifies stranded on all their projects. I think it is less resistance and runs cooler, I'm probably way off base with my assumption but it does sound good me.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#9
In reply to #7

Re: Blueskysb

03/08/2011 5:45 AM

The higher the frequency, the more a stranded cable will exhibit resistance (Impedence in this case).

For a good lightning conductor, flat copper strips are normally used. They are solid, and flat giving more surface than a round conductor. Multistrands, even if the total periferal surface is greater than the equivalent cross sectional round solid cable, it will have a greater impedence and I think someone more involved in the calculations could help prove it. I am sure of this because I have had experience in the domain of transmitting high frequency in some industrial equipment and multistrand cable was attempted by a collegue who was surprised to find no power at the other end. replaced with a flat foil did the trick.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#10
In reply to #9

Re: Blueskysb

03/08/2011 10:26 AM

Thanks. Is that due to the twist in the stranded cable acting as a coil?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #10

Re: Blueskysb

03/08/2011 11:36 AM

I am not sure it is only the twist in the wire, but the fact that there will be capacitive values between the strands as the contact cannot be guarantied on all the length etc.

The twist will add some inductance, but mainly, the difference is also the irregular contacts between the strands that will increase the overall impedence at high frequencies. We need more expertise in the field from someone that has conducted research to pinpoint the most important factor that eventually adds impedence at higher frequencies.

Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#12

Re: Blueskysb

03/10/2011 3:19 AM

Can I ask where in S. Oregon? (I am originally from Klamath Falls). I also have a friend here in Vancouver who is a specialist in such things, and I believe he is a certified ARRL technical advisor. Go to wb7esv@arrl.net. Dave could answer your question quicker than you could ask it.

73s de

Bill NW7L

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dkwarner (2); LAA_Lucke (3); lyn (1); not so smart (1); rcrain (1); Sciesis2 (1); setho (3)

Previous in Forum: Voltage Optimisation   Next in Forum: Double Earthing

Advertisement