Conductor Size

03/08/2011 12:25 AM

How to decide the size of Conductor for Neutral Earthing & Body Earthing. Pls give the formula too

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Conductor Size

03/08/2011 12:40 AM

This has been discussed dozens if not hundreds of times on CR4; you can do a "Search all of CR4." There is more to it than some formulas, and there is no "the formula."

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Conductor Size

03/08/2011 12:42 AM

First you should know how much current will flow

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Nov 2010
Posts: 16
#3
In reply to #2

Re: Conductor Size

03/08/2011 1:03 AM

its a 3 Phase 750 KVA Generator

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Conductor Size

03/08/2011 1:08 AM

In that case, knowing the voltage might be first....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Nov 2010
Posts: 16
#8
In reply to #4

Re: Conductor Size

03/18/2011 5:41 AM

voltage will be 415, frequency 50 Hz, PF 0.8

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Conductor Size

03/08/2011 9:38 AM

Assuming that it is a 415V generator, the following are the recommended earthing conductor sizes:

Neutral Earthing:

i) 1 1/2" x 1/4" (40mm x 6mm) Electrolytic Bare Copper Conductor or Strip

OR

ii) 2 x 225 sq.mm or 1 x 500 sq.mm PVC Insulated Single Core Stranded Aluminium Conductor

Body Earthing:

i) 1" x 1/8" (25mm x 3mm) Bare Copper

OR

ii) 185 sq.mm PVC Insulated Stranded Aluminium

OR

iii) 2" x 1/4" (50mm x 6mm) Galvanised Iron

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2010
Posts: 16
#9
In reply to #5

Re: Conductor Size

03/18/2011 5:43 AM

how we can calculate this

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10
In reply to #9

Re: Conductor Size

03/20/2011 9:59 AM

If you want to actually do the sizing very precisely, then you have to calculate the fault current at the motor terminal for a single-line-to-ground fault, duly taking into account the fault contributors and all the network impedances in line upto the point of fault. Then you calculate the conductor sizing by following the maximum permissible current density for the material chosen.

But, as there would be number of motors in an industry, it is a laborious process to undertake such an excercise. So, engineers' associations have given a ready-reckoner, assuming the nomimnal cable sizes used for the given HP/kVA. The above recommendation is from one such ready-reckoner.

Register to Reply
Associate
Netherlands - Member - New Member Canada - Member - New Member

Join Date: Oct 2010
Location: Canada
Posts: 41
Good Answers: 2
#11
In reply to #9

Re: Conductor Size

03/20/2011 3:22 PM

In many jurisdictions, the local codes will prescribe the minimum conductor size to use. These sizes are based on standard motors and/or other loads and will suffice for virtually all applications..

__________________
I do not feel obliged to believe that the same God who has endowed us with sense, reason, and intellect has intended us to forgo their use. Galileo Galilei
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Conductor Size

03/08/2011 11:39 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate
Netherlands - Member - New Member Canada - Member - New Member

Join Date: Oct 2010
Location: Canada
Posts: 41
Good Answers: 2
#7

Re: Conductor Size

03/08/2011 8:56 PM

Canadian Electrical Code, table 16.

__________________
I do not feel obliged to believe that the same God who has endowed us with sense, reason, and intellect has intended us to forgo their use. Galileo Galilei
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (2); jk (2); maddy1157 (3); pnaban (1); PWSlack (1); Tornado (2)