VFD on a 480 Volt Open Delta Utility Service

04/06/2007 4:43 PM

Has anyone experienced trouble with designing VFD's on a Open Delta utility?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2006
Location: SE MI USA
Posts: 105
#1

Re: VFD on a 480 Volt Open Delta Utility Service

04/07/2007 7:49 AM

i don't have any direct experience with it but reading this link indicates you may have to derate the rated available power by as much as 58%.

Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#2

Re: VFD on a 480 Volt Open Delta Utility Service

04/07/2007 10:46 AM

Could have a problem with third harmonic ,:it depends to load and the rest of the diagram configuration.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: VFD on a 480 Volt Open Delta Utility Service

04/08/2007 12:00 AM

Depends on the VFD in question. Some cannot be used on ungrounded delta systems, open or not. You need to check with the manufacturer.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster
#4

Re: VFD on a 480 Volt Open Delta Utility Service

04/10/2007 11:45 AM

The open delta system de-ration involves the transformers not the VFD.

The use of open delta , as seen , in some cheep sevices does not dirctly affect the rating of the VFD , but ... it is a direct threat to the VFD in terms of power anomilies , spikes , surges , harmonics , etc.

My recommendation is don't but if not possible to avoid use spike protection in 2x quantitys and best is to use a "12 pulse" 3 to 6 phase transformer ahead of it.

I have done many of these units and open delta is a bad service to use for any thing

Jon