Bonding Wire Question

03/21/2011 8:54 AM

Hi,

Anyone please explains to me why we need a bonding wire between the two flanges while we already had many bolts secured to ensure the continuity.

Regards,

__________________
Anything that can go wrong, will go wrong
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Bonding wire question

03/21/2011 9:02 AM

Fixing bolts cannot be relied upon always to provide good electrical continuity - if surface treatments are used, for example. Usually they'll be OK, but not always. That's why it's specified in the regulations - to make sure it will work in 100% of the cases.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Bonding Wire Question

03/21/2011 10:42 AM

Ever see the aftermath of an internal exposition in ductwork?

It's one hell of a mess to sort out. I've worked with pulverised coal it's frightening when it goes bang.

The straps are to stop static build up between sections.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: Bonding Wire Question

03/21/2011 11:50 AM

Just as a follow on to above:

Someone had the brilliant idea of vacuuming coal spillage. Great idea, but they didn't use conductive hose. It didn't explode, just caught fire.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#4

Re: Bonding Wire Question

03/21/2011 10:29 PM

The numerous points of contact between bolt and flange, nuts etc, over time will oxidize and become low grade semiconductor junctions here and there. Stray RF fields will get rectified and create random noise. If there is a welded continuous path between the metals, this will be prevented. The actual nuts themselves will still do this, but this will not be a problem compared to metals doors and runs of pipe.

People who make RF shielded rooms know all about 'debuzzing' of these rooms - any bits of metal not well connected.

__________________
Per Ardua Ad Astra
Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#5

Re: Bonding Wire Question

03/22/2011 12:55 AM

Hi hien,

Most or usually bonding wire made into flexible, therefore any movement on your pipe will not cause loose on grounding and delivered 100% continuity.

Cheers mate.

Roman

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#6

Re: Bonding Wire Question

03/22/2011 10:22 AM

To guarantee the correct flow of current you use bonding jumpers on flanges, remember that the bolts under tension will have slightly differing electrical conductivity, plus you will have gaskets as well as myabe insulated washers. So to avoid all the issues, you use bonding jumpers, safer and guaranteed

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Bonding Wire Question

03/27/2011 11:17 AM

If a star washer is placed between the underside of the head of the bolt and the flange, and another between the underside of the head of the nut and the other flange, then a bonding wire is unnecessary.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#8
In reply to #7

Re: Bonding Wire Question

03/27/2011 11:24 AM

partially true, a star washer under the correct tension will bite through insulating oxides - at first-, but as time goes by, thermal cycles, humidity, condensations cause this formerly gas tight connection to inexorably corrode and degrade, in time becoming a resistive connection, or worse, a rectifying one.

Where RF noise is not a problem, who cares, but for shielded rooms, bond everything

__________________
Per Ardua Ad Astra
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Bonding Wire Question

03/28/2011 7:10 AM

..........which will be fine for preventing the build-up of static electricity on the pipeline, which is where the technique is often used.

British Standard 7671 requires equipotential bonding for non-double-insulated equipment via the incoming power cable or via a supplementary earth wire.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aurizon (2); JohnDG (1); PWSlack (2); Roman (1); TonyS (2); vargaalex (1)

Previous in Forum: Equivalent Star Capacitance   Next in Forum: 13.8kv Switchgear Primary Contact Terminal Taping

Advertisement