what is meant by Residual Current? and how it can be tested?

__________________
dineshbe
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Residual Current

03/21/2011 12:34 PM

Exactly what it means in the dictionary sense :

When you vectorially add three-phase+neutral currents, (using a CBCT) the 'residue' should be zero. If it is not, that is the residual current and is flowing to earth through damaged insulation perhaps. Baaad news.

Search CR4, you will find plenty of threads on it.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3
In reply to #1

Re: Residual Current

03/22/2011 12:42 AM

How do you measure the leakage current in an equipment?.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Residual Current

03/27/2011 11:13 AM

Why measure <rhetorical question>? Just protect the user with an appropriately-rated residual current circuit breaker in accordance with British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5
In reply to #4

Re: Residual Current

03/28/2011 1:11 AM

If leakage current is not given in the nameplate of a machine or home/office appliance we might overload {the tripping current(mA)}a circuit. Consider a 30mA 2P RCD used to protect 20nos PCs in a school connected in a ring circuit. If leakage current of a PC exceed 1mA the leakage current will be 20mA for which RCD will not trip but it exceeds the 50% rated tripping current of RCD,which the circuit should withstand. That's why I have said leakage current,no load/LR current of motors,THD,PF etc to be included in the nameplate.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Residual Current

03/28/2011 7:05 AM

Leakage/residual current indicates a fault. The trip settings are there to prevent electrocution in the first instance, and to operate the circuit protective device(s).

What is the nature of the fault in each of 20 PCs that merits the measurement of it? Why not just rectify the fault in each one and be done with it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #6

Re: Residual Current

03/28/2011 10:44 AM

Without a fault there could be a leakage current in components used in a machine if not manufactured to high standards.

__________________
pnaban
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Residual Current

03/21/2011 9:21 PM

When the current going out does not equal the current coming back the difference between the two is the residual current. Googling provides a decent answer and some animations that illustrate the concept. http://en.wikipedia.org/wiki/Residual-current_device.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

kvsridhar (1); pnaban (3); PWSlack (2); RAMConsult (1)

Previous in Forum: Is Electrical Current or Voltage Harmful to Humans?   Next in Forum: 400HP vs. 200HP in Cost to Run

Advertisement